    Cooling Tower Question

    What are the Pros and Cons using One cooling tower with multiple cells Vs. individual cooling towers?
    Either way it feeds one common building riser.

  2. #2
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,520
    Double towers often have a single drain. So if you need to drain one side for service, you may have to dam-up the water on the other side, then manage the level controls too. Otherwise, they should be more cost effective and mainly have a smaller footprint. Similarly, if the drain gets plugged up, you lose capactiy on both cells.

    I would make sure that you can isolate and balance water to both sides of the tower. This way, if you do have a fill collapse of damage, you can isolate that side and at least get partial capacity while waiting for repairs. Some double towers just have a single valve to distribute water to both sides of a single cell.

  3. #3
    Join Date
    Aug 2009
    Location
    Jurupa Valley, CA
    Posts
    1,781
    Pros: Cost - twinned towers are cheaper than their single counterparts for the capacity.
    Cons: Sharing of water basin means cannot shut down 1 cell for cleaning/maintenance usually means losing two.

    If it is a large plant, where there are, say, 6 cells needed, I see no problem, and would actually recommend the twinned variety. In that case, taking 2 cells down to work on 1 is not as major an issue.

  4. #4
    Join Date
    Jul 2012
    Location
    New York
    Posts
    6
    To add more into the fact is there are Three (3) Marley 550 ton each towers and There will be filtration system. Even if they combined will have separate drains, valves and power.
    Is there any performance issues other than cleaning and leveling?

  5. #5
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,520
    Quote Originally Posted by CraziFuzzy View Post
    Cons: Sharing of water basin means cannot shut down 1 cell for cleaning/maintenance usually means losing two.
    It does depend largely on the tower specs. Some even have multiple drains. Others, as I've mentioned, have a drain towards the center and you may have luck using sandbags to block off one side.

    But in general, this is the major disadvantage.

  6. #6
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,350
    Quote Originally Posted by Mechcontr View Post
    To add more into the fact is there are Three (3) Marley 550 ton each towers and There will be filtration system. Even if they combined will have separate drains, valves and power.
    Is there any performance issues other than cleaning and leveling?
    Are they forced or induced draft towers?

    Recirculation of tower exhaust can be a concern in some installations.

    Treat the water right for scale, algae, corrosion, and legionella.
    • Electricity makes refrigeration happen.
    • Refrigeration makes the HVAC psychrometric process happen.
    • HVAC pyschrometrics is what makes indoor human comfort happen...IF the ducts AND the building envelope cooperate.


    A building is NOT beautiful unless it is also comfortable.

  7. #7
    Join Date
    Jul 2012
    Location
    New York
    Posts
    6
    Quote Originally Posted by Shophound View Post
    Are they forced or induced draft towers?

    Recirculation of tower exhaust can be a concern in some installations.

    Treat the water right for scale, algae, corrosion, and legionella.
    they are induced draft towers.

  8. #8
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,718
    Bizmo66

    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.

    Your post has been deleted

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event