Thread: External Equalizer Line Ices Up
-
07-16-2012, 12:52 PM #1
Regular Guest
- Join Date
- Feb 2010
- Location
- New York City
- Posts
- 46
External Equalizer Line Ices Up
10 Ton Scroll Compressor, R-22 AIR Conditioner
Suction: 51 P.S.I. Discharge: 200 P.S.I.
Condenser water in :75 Degrees
Air Temp entering evap coil :74 Deg
Evap Coil Clean, good air flow across coil
14 Degree :split air across evap coil ( This delta T is normal for these units)
New Power head on expansion valve
I throttled down on the TXV
Superheat measured at suction line feeler bulb : 20 Degrees
I may be overcharged. The suction line and half compressor are really sweating back
There is good amount of foam in the oil sight glass
I gather there is liquid boiling off in the External Equal. Line
Why would the suction pressure be so low?
-
07-16-2012, 05:03 PM #2
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 946
whats the leaving water temp? at 51psi the evap must be iced up, your measurement are kind of screwy
-
07-16-2012, 06:46 PM #3
It seems to me that you have liquid refrigerant flowing through your equalizing line which is giving your TX valve a false evaporator pressure. I'd start with a new TX valve, JMHO.
-
07-16-2012, 06:56 PM #4
That sounds like an internal leak in the valve,was it doing that before you changed the power head?
-
07-16-2012, 09:38 PM #5
-
07-16-2012, 10:38 PM #6
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
What about a restriction in that equalizer line
-
07-16-2012, 10:57 PM #7
Professional Member*
- Join Date
- Oct 2009
- Location
- God's country - Shenandoah Valley, VA
- Posts
- 195
-
07-17-2012, 06:09 AM #8
-
07-17-2012, 07:37 AM #9
I have seen where the leak at the pushrods is small,just enough to hit the power head and back the valve off.
-
07-17-2012, 02:34 PM #10The picture in my avatar is of the Houston Ship Channel and was taken from my backyard. I like to sit outside and slap mosquitos while watching countless supertankers, barges and cargo ships of every shape and size carry all sorts of deadly toxins to and fro. It's really beautiful at times.....just don't eat the three eyed fish....
¯`·.¸¸ .·´¯`· .¸>÷÷(((°>
`·.¸¸..· ´¯`·.¸ ¸.·´¯` ·.¸>÷÷(((°>
.·´¯`· .¸>÷÷(((°>
LMAOSHMSFOAIDMT
-
07-20-2012, 11:46 PM #11
Rebuilding the valve will typically not solve this problem. Most TEVs do not have packings to provide the seal between the pushrods and pushrods hole...there are a few exceptions. The seal is a function of the clearance between the pushrod diameter and the pushrod hole diameter. If the clearance between the two is excessive you will have leakage.
Since all machined parts have a +/- tolerance, there is no telling if the pushrods contained in the parts kit will actually be of a diameter which will prevent the leakage.
Additionally, if a valve is rebuilt, the pushrods will need to be filed down to the proper length (by measuring the pushrod height above the top of the valve, using a pushrod gauge). All pushrods in parts kits are purposefully too long...neglecting to file them down will increase the valve stroke, causing a capacity increase.
Replace the valve.