    Hello, I have a Mc Quay unit that has two circuits on it.

    Each circuit has two compressors on it, 6 stages of

    cooling. My problem is that the #1 circuit trips out on me

    and I have to turn the circuit off and on to reset it. The

    coils are flushed out and the 2nd circuit comes on and off

    no problem. My Pressures yesterday on the 1 circuit was

    76 low and 200 high on a 77 degree day with only one

    compressor running. With two compres. my press. are 63 low

    and 235 high. Does anybody have any ideas? Thanks.


  2. #2
    Join Date
    Jul 2006
    Posts
    57
    Post Likes
    Check your airflow. If not that, what is your SH at full load on that circuit? Your shutting down on LP more that likely.

  3. #3
    Join Date
    Feb 2006
    Location
    Lexington, Ky
    Posts
    169
    Post Likes
    What is the model of the machine?

    Is it a chiller or DX?

    What kinds of compressors and how many?

    Need more info.

  4. #4
    Join Date
    Aug 2006
    Posts
    19
    Post Likes
    Thread Starter
    Hello, figured it out today. I had a guy find that the HP

    switch was cutting it out. A bad switch. It is a little

    low on freon. Sorry I didn't have that much info but

    thanks for your help.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •