I have a Microset with Temp and Humidity display.
The temp is AI-0 to AV point but the humidity is straight to AV point.
How can I calibrate it so the display can show the
right humidity reading?
TIA
-
Few questions that will help with answering your question.
Are you using a Microset or Microset II?
MS/TP. Yes or no?
What exactly are you looking to do?
As far as I know, Space Humidity is done by a read-only value AV-102. Also, the BV to display space humidity on the microset is BV-84.
I will check back sometime today or tomorrow.
-
 Originally Posted by chrisfiander
Few questions that will help with answering your question.
Are you using a Microset or Microset II?
MS/TP. Yes or no?
What exactly are you looking to do?
As far as I know, Space Humidity is done by a read-only value AV-102. Also, the BV to display space humidity on the microset is BV-84.
I will check back sometime today or tomorrow.
Microset II and MSTP
Looking to calibrate the humidity value.
It is 10% off.
I can take the AV-102 and put an offset in programming for control purposes but the display still reads wrong.
TIA