    Low head, normal suction, HIGH amps

    5 ton scroll compressor in a split system.

    Suction ~40psig
    Discharge ~210psig
    Amps 30+A
    Superheat ~17

    It is a 3 phase compressor, pulls 30 amps from the get go and will go all the way to 40 amps (and shut off)

    The winding(s) resistance is about .5 ohms on all of them. It also doesnt sound great when it is running. I recovered 20 pounds of refrigerant from this system, recharged with around 7.5 pounds... After cleaning the ridiculously dirty evaporator.

    Just looking for affirmation, thank you for your input.

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    7.5 pounds sounds low on a 5 ton split system.

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by wdshea View Post
    5 ton scroll compressor in a split system.

    Suction ~40psig
    Discharge ~210psig
    Amps 30+A
    Superheat ~17

    It is a 3 phase compressor, pulls 30 amps from the get go and will go all the way to 40 amps (and shut off)

    The winding(s) resistance is about .5 ohms on all of them. It also doesnt sound great when it is running. I recovered 20 pounds of refrigerant from this system, recharged with around 7.5 pounds... After cleaning the ridiculously dirty evaporator.

    Just looking for affirmation, thank you for your input.
    Did you measure amps on all 3 legs?



  4. #4
    Join Date
    Apr 2007
    Location
    T.C minnesota
    Posts
    12
    Post Likes
    I'm guessing R-22. If so looks like low suction, normal head. more info would help. I like to megaohm the compressor to ensure the windings are good.

  5. #5
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    split unit what was the ambient around the condenser 210PSI air cooled is low for R-22.how is the condenser on being clean...flush it inside out.... is this a commercial site strip mall or residence?
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  6. #6
    Join Date
    Sep 2011
    Posts
    95
    Post Likes
    Thread Starter
    Im sorry, i was thinking of my suction saturation when i said 40, pressure was around 69psig on the suction. Yes i checked all three legs. I cleaned the condenser twice. This is commercial.

    Megaohm the windings to ground?

  7. #7
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    You can use a megger if you have one. Isolate the leads from the compressor and megg from the compressor terminals to ground.

  8. #8
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    typically, a short to ground is not going to cause high running amperage.

    That would be more likely to cause high instantaneous amperage and result in a breaker trip.

    I would leave the megger in the truck here.

    I'd look for a performance curve on that pump and see what the manufacturer says that it SHOULD draw under those conditions.

    I suspect that you'll be replacing a compressor, soon, though.



  9. #9
    Join Date
    Sep 2011
    Posts
    95
    Post Likes
    Thread Starter
    The olp trips pretty quick, it never pulls less than 30 amps, so it only runs about 5 minutes, if that. I thought that maybe a previous tech may have the motor running backwards, so i switched some leads. AmP draw went to 12A but the compressor sounded like hell, so i'm certain it was running the right way.

  10. #10
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by wdshea View Post
    The olp trips pretty quick, it never pulls less than 30 amps, so it only runs about 5 minutes, if that. I thought that maybe a previous tech may have the motor running backwards, so i switched some leads. AmP draw went to 12A but the compressor sounded like hell, so i'm certain it was running the right way.
    A grounded winding will typically pop the breaker/overload instantly, not over a couple of minutes.



  11. #11
    Join Date
    Sep 2011
    Posts
    95
    Post Likes
    Thread Starter
    What else could this be? I was thinking shorted windings

  12. #12
    Join Date
    Jul 2012
    Location
    central VA
    Posts
    229
    Post Likes
    What is the LRA and what is the compressor rated at? 30 plus amps sounds high in a 5 ton system.
    I rather do nothing and be happy than to do something and not be happy

  13. #13
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    My guess would be the bearing are going bye bye. 30 amps on a 5 ton 3 phase compressor? Not long for this world!
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  14. #14
    Join Date
    Sep 2011
    Posts
    95
    Post Likes
    Thread Starter
    RLA 20A
    LRA 120A

  15. #15
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    Thats what happens when you run twice the correct charge with a dirty evap!
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  16. #16
    Join Date
    Jul 2012
    Location
    central VA
    Posts
    229
    Post Likes
    If its pulling high amps then condemn the compressor
    I rather do nothing and be happy than to do something and not be happy

  17. #17
    Join Date
    Jul 2012
    Location
    central VA
    Posts
    229
    Post Likes
    Its a matter of time before it fails
    I rather do nothing and be happy than to do something and not be happy

  18. #18
    Join Date
    Jun 2009
    Posts
    59
    Post Likes
    Check your volts when running? Bad contacor breaker disconnect? Tighten all connections check voltage drops across them and temps..

  19. #19
    Join Date
    Jan 2010
    Location
    Oklahoma City
    Posts
    174
    Post Likes
    Quote Originally Posted by jimj View Post
    My guess would be the bearing are going bye bye. 30 amps on a 5 ton 3 phase compressor? Not long for this world!
    What he said. I had one start at normal amps then climb as it ran until it tripped. Boss thought I was crazy changing compressor but had no other ideas, then was happy when it fixed the issue.

  20. #20
    Join Date
    Jul 2012
    Location
    Southwest
    Posts
    114
    Post Likes
    It could be oil return. If you dont draw the oil back your amps will rise as it runs. It may start normal then rise up. I would be thinking that route.
    I have heard some will mix in some POE to help draw mineral back?

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •