Results 1 to 4 of 4
  1. #1
    Join Date
    Jul 2012
    Posts
    14
    Post Likes

    boiler pipe size

    i am just curious but can an 1 1/4'' pipe be able to support 15 zones with 14 of them all pumping 2 GPM to fan coils all at once through 1/2'' pipes? like is it even possible? i am going to hire a contractor but was curious about this.

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    75,910
    Post Likes
    Not really.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    May 2012
    Location
    San Diego, CA
    Posts
    352
    Post Likes
    It is possible but you are looking at water velocities of 7 ft per sec and a lot of friction loss... about 8 psi per every 100 ft of pipe.

    Go with at least a 1 1/2" L copper pipe and size accordingly.

    I would recommend not passing 6 ft per sec... international code recommends as low as 5 ft per sec.

    Sizing Charts:
    http://publicecodes.citation.com/ico...ppe_sec003.htm
    http://www.iapmo.org/2010%20Californ...pendix%20A.pdf
    You can call me Sam

    It should be a crime to be a mechanical engineer in San Diego
    Summer Design Temperature: 83 F Dry Bulb ~ 69 F Wet Bulb (California Climate Zone 7)

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    75,910
    Post Likes
    In boiler piping for comfort heating, 1-1/4" copper generally tops out at 16GPM.

    To get the 30 GPM he would need. He would need to use a circ capable of moving 30GPM at a head of about 20 foot just for the 1-1/4" primary loop including the fittings. Which would put him needing something in a Taco 1611 model.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.