    Jul 2012
    boiler pipe size
    i am just curious but can an 1 1/4'' pipe be able to support 15 zones with 14 of them all pumping 2 GPM to fan coils all at once through 1/2'' pipes? like is it even possible? i am going to hire a contractor but was curious about this.
    Not really.
    May 2012
    San Diego, CA
    It is possible but you are looking at water velocities of 7 ft per sec and a lot of friction loss... about 8 psi per every 100 ft of pipe.
    Go with at least a 1 1/2" L copper pipe and size accordingly.
    I would recommend not passing 6 ft per sec... international code recommends as low as 5 ft per sec.
    Sizing Charts:
    http://publicecodes.citation.com/ico...ppe_sec003.htm
    http://www.iapmo.org/2010%20Californ...pendix%20A.pdf
    You can call me Sam
    It should be a crime to be a mechanical engineer in San Diego
    Summer Design Temperature: 83 F Dry Bulb ~ 69 F Wet Bulb (California Climate Zone 7)
    In boiler piping for comfort heating, 1-1/4" copper generally tops out at 16GPM.
    To get the 30 GPM he would need. He would need to use a circ capable of moving 30GPM at a head of about 20 foot just for the 1-1/4" primary loop including the fittings. Which would put him needing something in a Taco 1611 model.