    My a/c treats every day like a 100 degree day!

    First of all, many thanks to those who responded to a question I had several weeks ago. I followed your advice and got an energy audit done.

    Here's my current situation: I have a 3300 sq. ft. (with the basement), open floorplan home. The main floor and basement is heated and cooled by a Goodman gas furnace and a/c. The upstairs (fully exposed to the main floor) is heated and cooled by a Trane heat pump, 17 SEER. (I'm sorry that I don't know the sizes of these units.) The heat pump was just repaired (bad capacitor).

    My concern: No matter how mild the heat is outside, the upstairs runs constantly.

    On Thursday, with a local high temp (I live in Maryland) of only 87, my upstairs unit could not reach the set point of 78 degrees in the later afternoon after being set to 83 when we're at work. When I got home, I watched the thermostat read 81 degrees for 2.5 hours with the unit constantly running.

    On Friday, with a local high temp of only 81, I experimented with a set point of 74 degrees (after an "away" set point of 79 degrees). When I got home in the mid afternoon, I observed my unit run for 3 straight hours, but the thermostat temperature dropped down from only 79 to 77.

    On Saturday, with a local high of only 83 degrees, I set the thermostat to a steady 79 degrees all day. Even though the upstairs was actually kept at 79 all day, in the afternoon the upstairs unit was running almost constantly, with an approximate run time of 30 minutes followed by only a 5 minute off period before turning back on again.

    I'm not educated in these things, but common sense seems to tell me that these numbers might be appropriate for a 100 degree day, but not temperatures in the low 80s. The a/c company told me that both units are working great and that they are fully charged. They checked the ductwork and found no leaks. The energy audit revealed that my house is "tight" (and if I did any more tightening, I'd have to install a system to bring in more outside air to avoid the dangers of stale air or carbon monoxide). My insulation is adequate, my house having been built in 2000, but like most owners, I could always add more insulation. There are "typical" problems of some air leakage round the baseboads, outlets, etc.

    I have another company coming out Tuesday to look at the upstairs unit. What sort of things should I have them check? If we assume that the unit is working correctly and that my insulation is adequate, is there something else that could explain my unit working and working and working to get to or keep a set point not much cooler than the outside? Thanks so much!

  2. #2
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    4,963
    IMO, from what you have explained, -there has to be major problems with the upstairs situation.

    If U want some clues to what might be causing the problems, we need the temperatures & the humidity readings listed below:
    1) Helpful, Tonnage of Unit or outdoor condenser model number: _____
    2) TXV or, orifice metering device? _______ Only if U know.
    ==============
    3) Outdoor condenser’s discharge-air-temperature _____
    4) Outdoor air temperature: _______
    5) Outdoor Condenser air-Temp-split _____
    6) Need the percent of humidity - away from Supply-air outlets ______
    7) Indoor Return-Air Temperature ___ Supply-Air Temperature ______
    8) Indoor temperature-split _______

    Take all the readings during the same time period &, around 4:30 pm is the best time period as the heatload usually peaks during that time.

    One of the heat pump check-valves 'could be' sticking...only one possibility of many.
    Last edited by udarrell; 07-14-2012 at 09:52 PM. Reason: Typos...

  3. #3
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,520
    ONe other thing worth trying, don;t use setback, especially with with a 2 stage system. I ran some numbers the other day looking at system efficiency at different temperatures, and you use about 5-10% more energy using a setback with a 2 stage system. With a single stage, it's about 0-5%, but in the end, your not saving energy, and your home is less comfortable.

    The fact that on a 87F days, you upstairs gets to 81F, tells me you have a lot of heat in your attic and either poor insulation or inadequate venting.

    Try not using a setback in the afternoon and see if that improves your situation. IT does sound like you may have some performance issues on your upstairs system regardless. But I think heat in the attic is causing a lot of your problems. YOu may also have a lot of air leaks in the home bringing in outside air and heating it up and raising humidity.

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,875
    Has the upstairs always had this problem, or just recently.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    3,081
    how did the auditing company determine if your ductwork was not leaking? a ductblaster test is quite time and labor intensive. the temps you are reporting upstairs lead me to look into the attic infiltration of the upstairs.
    The TRUE highest cost system is the system not installed properly...
    The three big summer hearththrobs...
    Mel Gibson
    Dwane Johnson
    The A/C repairman