Thread: Low Subcooling Low Superheat?

  1. #21
    Join Date
    Dec 2008
    Location
    indiana
    Posts
    17
    Post Likes
    verify air flow using mini vane or equev.
    what is the amp draw at compresor
    is the evap coil / blower clean
    what is return wb and
    supply wb
    how did you figure capacity

  2. #22
    Join Date
    Dec 2011
    Location
    British Columbia, Canada
    Posts
    53
    Post Likes
    have you tried testing the txv by heating and cooling the bulb?

  3. #23
    Join Date
    Jan 2007
    Location
    Mn the state where absolutey nothing is allowed
    Posts
    2,516
    Post Likes
    its been 6 days, the OP hasnt been back, guess he fix it.?!?

    so we can all benefit, it'd be nice to here how these threads end up
    my boss thinks its possible to repeal the laws of physics

  4. #24
    Join Date
    Jan 2011
    Location
    Maryland
    Posts
    9
    Post Likes
    Thread Starter

    Fixed

    Sorry for the delaying in posting, While I was on vacation, another tech replaced the indoor coil. After replacement the system ran at spec's 12 deg s/c 9 deg of s/h. althought the coil would frost evenly when the blower was off. We ran out of options and replaced the coil. I am requesting an RMA back to Carrier to have the coil tested. If I get anything back I'll post thier finding.
    Thanks all

  5. #25
    Join Date
    Nov 2011
    Location
    USA
    Posts
    4,451
    Post Likes
    Quote Originally Posted by MIDCAM View Post
    We ran out of options and replaced the coil.
    Which options did you exercise?

  6. #26
    Join Date
    Jan 2011
    Location
    Maryland
    Posts
    9
    Post Likes
    Thread Starter

    tXV

    The TXV was changed from the factory Danfoss to a Sporland, The equalize line was check for flow. All checked good. Air flow was double checked by checking pressure drop a crossed the coil. .58”wc

  7. #27
    Join Date
    Jan 2011
    Location
    Maryland
    Posts
    9
    Post Likes
    Thread Starter
    the valve checked good the heat added and then dip into and ice bath, responsive to both

  8. #28
    Join Date
    Nov 2011
    Location
    USA
    Posts
    4,451
    Post Likes
    Quote Originally Posted by MIDCAM View Post
    The TXV was changed from the factory Danfoss to a Sporland, The equalize line was check for flow. All checked good. Air flow was double checked by checking pressure drop a crossed the coil. .58”wc the valve checked good the heat added and then dip into and ice bath, responsive to both
    Fair enough...for a while there, I thought you had burned down the house to get rid of the cockroaches.

  9. #29
    Join Date
    May 2009
    Location
    Jacksonville FL
    Posts
    4,581
    Post Likes
    Running low superheat and low subcool....txv stuck open.....you can add and add refrigerant....need new txv.

  10. #30
    Join Date
    May 2018
    Posts
    1
    Post Likes
    The same situation was happening to me: 410-A condenser, Low SuC and Low SuH, i struggled to find out why. A super dirty conders coil and air in system where 2 things that pop in my head. Coil was not dirty and gauges did not show signs of air (noncondensible). I read the $&@n manual where it asked for Service Access door to be attached while checking pressures so as not to deprive coil of air flow and all my pressures were perfect. Hope this does not happen to anyone. 🖖

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •