Txv stuck open
-
07-15-2012, 09:37 PM #15
TXV problem
-
07-16-2012, 01:21 AM #16
Regular Guest
- Join Date
- Jan 2012
- Location
- Fresno, ca
- Posts
- 30
Read the book on that cond. Unit. I know with some Carriers, they have to be running in high capacity or you'll get funny pressure reading. Also check if the indoor blower is running in high speed.
-
07-16-2012, 11:40 AM #17
Sounds like more air flow is needed to me.
As iron sharpens iron so one man sharpens another Proverbs 27:17 NIV84
-
07-16-2012, 06:07 PM #18
Professional Member*
- Join Date
- Feb 2010
- Location
- IL
- Posts
- 113
TXV Problem, Airflow is good at 700 CFM for a 2 ton. Newer systems call 350 CFM better dehumidification. Seems stuck open.
-
07-16-2012, 09:34 PM #19
Professional Member
- Join Date
- Jan 2007
- Location
- Mn the state where absolutey nothing is allowed
- Posts
- 1,084
-
07-17-2012, 11:21 PM #20
Professional Member*
- Join Date
- Oct 2009
- Location
- Florida
- Posts
- 143
I believe your compressor is still in first stage. IIRC there's a five minute delay from signal sent to compressor engage in addition to the delays in some thermostats. I've seen those same pressure/temp/sh/sc conditions on a carrier two stage system that would not engage full capacity.
-
07-19-2012, 07:22 PM #21
Regular Guest
- Join Date
- Dec 2008
- Location
- indiana
- Posts
- 16
verify air flow using mini vane or equev.
what is the amp draw at compresor
is the evap coil / blower clean
what is return wb and
supply wb
how did you figure capacity
-
07-20-2012, 01:41 AM #22
Regular Guest
- Join Date
- Dec 2011
- Location
- British Columbia, Canada
- Posts
- 51
have you tried testing the txv by heating and cooling the bulb?
-
07-20-2012, 06:32 PM #23
Professional Member
- Join Date
- Jan 2007
- Location
- Mn the state where absolutey nothing is allowed
- Posts
- 1,084
its been 6 days, the OP hasnt been back, guess he fix it.?!?
so we can all benefit, it'd be nice to here how these threads end upmy boss thinks its possible to repeal the laws of physics
-
07-29-2012, 04:40 PM #24
Regular Guest
- Join Date
- Jan 2011
- Location
- Maryland
- Posts
- 9
Fixed
Sorry for the delaying in posting, While I was on vacation, another tech replaced the indoor coil. After replacement the system ran at spec's 12 deg s/c 9 deg of s/h. althought the coil would frost evenly when the blower was off. We ran out of options and replaced the coil. I am requesting an RMA back to Carrier to have the coil tested. If I get anything back I'll post thier finding.
Thanks all
-
07-29-2012, 08:47 PM #25
Regular Guest
- Join Date
- Nov 2011
- Location
- USA
- Posts
- 184
-
07-29-2012, 09:46 PM #26
Regular Guest
- Join Date
- Jan 2011
- Location
- Maryland
- Posts
- 9
tXV
The TXV was changed from the factory Danfoss to a Sporland, The equalize line was check for flow. All checked good. Air flow was double checked by checking pressure drop a crossed the coil. .58wc