Thread: Low Subcooling Low Superheat?

  1. #1
    Join Date
    Jan 2011
    Location
    Maryland
    Posts
    9
    Post Likes

    Low Subcooling Low Superheat?

    I am working on a two stage heat pump with a varable speed air handler.
    The system runs about 1.5 deg S/C and about 2 deg S/H The delta T is 22 deg. A capacity check shows systems is operation at 122% of publish Capacity. Adding refregerant does not change the S/C much at all.
    My question is how is this possable? low subcooling and low S/H
    This is a matched system, and all test equiment was checked for accuarcy.

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Moved to Tech to Tech residential



  3. #3
    Join Date
    Jun 2004
    Posts
    946
    Post Likes
    Is the compressor and evap motor at 100% ?
    What kind of airflow to your air handler?

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    You've got multiple problems, I think.

    Please provide all of the readings that you took on the unit along with model and serial and maybe we can see a problem.



  5. #5
    Join Date
    Jan 2011
    Location
    Maryland
    Posts
    9
    Post Likes
    Thread Starter
    25HNB624 with an FE4ANF003 Air Handler.
    90 deg ODBD Pressures 298/138# liquid line@ service valve 93deg vapor @ service valve 52 deg.
    air flow @ 700 CFM +/- 20 cfm
    RA 76 deg db 67 Deg wb
    SA 54 deg db 52 Deg wb

  6. #6
    Join Date
    Jan 2011
    Location
    Maryland
    Posts
    9
    Post Likes
    Thread Starter
    Compressor @ 60% of fla air flow @ 700cfm

  7. #7
    Join Date
    Jul 2004
    Location
    Massachusetts
    Posts
    6,846
    Post Likes
    You may have a flooded everything due to a gross overcharge. Start by recovering all the refrigerant from the system. The start with a fresh charge to factory specs and see where things are at that point.
    If YOU want change, YOU have to first change.

    If you are waiting for the 'other guy' to change first, just remember, you're the 'other guy's' other guy. To continue to expect real change when you keep acting the same way as always, is folly. Won't happen. Real change will only happen when a majority of the people change the way they vote!

  8. #8
    Join Date
    Jan 2011
    Location
    Maryland
    Posts
    9
    Post Likes
    Thread Starter
    The Refrigerant charge was recovred and weight back in @ factory specs added 5 lbs more. and removed 10lbs. still little change is s/c

  9. #9
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by MIDCAM View Post
    The Refrigerant charge was recovred and weight back in @ factory specs added 5 lbs more. and removed 10lbs. still little change is s/c

    I would have loaded just the factory spec amount and continued the diag from there. No need to add 5 more lbs....
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  10. #10
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Where, exactly, are you measuring the liquid line pressure and temperature?

    Where, in relationship to the liquid drier?



  11. #11
    Join Date
    May 2007
    Location
    Central NJ Area
    Posts
    1,248
    Post Likes
    I'm guessing it's metered by a txv? Could the txv be causing the issue?

  12. #12
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by MIDCAM View Post
    The Refrigerant charge was recovred and weight back in @ factory specs added 5 lbs more. and removed 10lbs. still little change is s/c
    No offense, but a part of me is questioning your instruments.

    I just can't see adding 5 pounds of refrigerant without affecting subcooling unless you have an extraordinarily long lineset.



  13. #13
    Join Date
    Jan 2011
    Location
    Maryland
    Posts
    9
    Post Likes
    Thread Starter
    As did I with three different instruments A cooper digital. Field Piece digital. And my old standby yellow jacket and fluke temperature probes. Nothing makes sense. How can a evap show flooded and the condenser be starved?

  14. #14
    Join Date
    May 2007
    Location
    Central NJ Area
    Posts
    1,248
    Post Likes
    Txv stuck open

  15. #15
    Join Date
    Jul 2012
    Location
    central VA
    Posts
    229
    Post Likes
    TXV problem
    I rather do nothing and be happy than to do something and not be happy

  16. #16
    Join Date
    Jan 2012
    Location
    Fresno, ca
    Posts
    47
    Post Likes
    Read the book on that cond. Unit. I know with some Carriers, they have to be running in high capacity or you'll get funny pressure reading. Also check if the indoor blower is running in high speed.

  17. #17
    Join Date
    Jun 2007
    Location
    Greenwood Indiana (Indianapolis)
    Posts
    420
    Post Likes
    Sounds like more air flow is needed to me.
    As iron sharpens iron so one man sharpens another Proverbs 27:17 NIV84

  18. #18
    Join Date
    Feb 2010
    Location
    IL
    Posts
    141
    Post Likes
    TXV Problem, Airflow is good at 700 CFM for a 2 ton. Newer systems call 350 CFM better dehumidification. Seems stuck open.

  19. #19
    Join Date
    Jan 2007
    Location
    Mn the state where absolutey nothing is allowed
    Posts
    2,516
    Post Likes
    Quote Originally Posted by MIDCAM View Post
    I am working on a two stage heat pump with a varable speed air handler.
    The system runs about 1.5 deg S/C and about 2 deg S/H The delta T is 22 deg. A capacity check shows systems is operation at 122% of publish Capacity. Adding refregerant does not change the S/C much at all.
    My question is how is this possable? low subcooling and low S/H
    This is a matched system, and all test equiment was checked for accuarcy.
    Quote Originally Posted by skidoox800 View Post
    TXV Problem, Airflow is good at 700 CFM for a 2 ton. Newer systems call 350 CFM better dehumidification. Seems stuck open.

    the only way he's getting 122% rated capacity is that there is actually less airflow than the number he used in the capacity calculation.
    my boss thinks its possible to repeal the laws of physics

  20. #20
    Join Date
    Oct 2009
    Location
    Florida
    Posts
    201
    Post Likes
    I believe your compressor is still in first stage. IIRC there's a five minute delay from signal sent to compressor engage in addition to the delays in some thermostats. I've seen those same pressure/temp/sh/sc conditions on a carrier two stage system that would not engage full capacity.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •