Page 3 of 3 FirstFirst 123
Results 27 to 29 of 29
  1. #27
    Join Date
    Jan 2011
    Location
    Maryland
    Posts
    9
    Post Likes
    the valve checked good the heat added and then dip into and ice bath, responsive to both

  2. #28
    Join Date
    Nov 2011
    Location
    USA
    Posts
    1,282
    Post Likes
    Quote Originally Posted by MIDCAM View Post
    The TXV was changed from the factory Danfoss to a Sporland, The equalize line was check for flow. All checked good. Air flow was double checked by checking pressure drop a crossed the coil. .58”wc the valve checked good the heat added and then dip into and ice bath, responsive to both
    Fair enough...for a while there, I thought you had burned down the house to get rid of the cockroaches.

  3. #29
    Join Date
    May 2009
    Location
    Jacksonville FL
    Posts
    4,595
    Post Likes
    Running low superheat and low subcool....txv stuck open.....you can add and add refrigerant....need new txv.