    I am working on a two stage heat pump with a varable speed air handler.
    The system runs about 1.5 deg S/C and about 2 deg S/H The delta T is 22 deg. A capacity check shows systems is operation at 122% of publish Capacity. Adding refregerant does not change the S/C much at all.
    My question is how is this possable? low subcooling and low S/H
    This is a matched system, and all test equiment was checked for accuarcy.
    Is the compressor and evap motor at 100% ?
    What kind of airflow to your air handler?
    You've got multiple problems, I think.
    Please provide all of the readings that you took on the unit along with model and serial and maybe we can see a problem.
    Jan 2011
    Maryland
    25HNB624 with an FE4ANF003 Air Handler.
    90 deg ODBD Pressures 298/138# liquid line@ service valve 93deg vapor @ service valve 52 deg.
    air flow @ 700 CFM +/- 20 cfm
    RA 76 deg db 67 Deg wb
    SA 54 deg db 52 Deg wb
    Jan 2011
    Maryland
    Compressor @ 60% of fla air flow @ 700cfm
    Massachusetts
    You may have a flooded everything due to a gross overcharge. Start by recovering all the refrigerant from the system. The start with a fresh charge to factory specs and see where things are at that point.
    Jan 2011
    Maryland
    The Refrigerant charge was recovred and weight back in @ factory specs added 5 lbs more. and removed 10lbs. still little change is s/c
    Southeastern Pa
    Quote Originally Posted by MIDCAM View Post
    I would have loaded just the factory spec amount and continued the diag from there. No need to add 5 more lbs....
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Where, exactly, are you measuring the liquid line pressure and temperature?
    Where, in relationship to the liquid drier?
    Central NJ Area
    I'm guessing it's metered by a txv? Could the txv be causing the issue?
    No offense, but a part of me is questioning your instruments.
    I just can't see adding 5 pounds of refrigerant without affecting subcooling unless you have an extraordinarily long lineset.
    Jan 2011
    Maryland
    As did I with three different instruments A cooper digital. Field Piece digital. And my old standby yellow jacket and fluke temperature probes. Nothing makes sense. How can a evap show flooded and the condenser be starved?