    hello experts,

    i just got a simple question. If an AHU frame is aluminum extrusion frame, is it possible to leave those frames without any insulation from inside? (fiberglass or polyurethane foam insulation). Besides, nothing like cold-bridge or thermal break is applied.

    The AHU is double walled with polyurethane foam insulation.

    how bad can that be? or its ok?

  2. #2
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    8,441
    Post Likes
    Climate region and more detail on the construction?
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  3. #3
    Join Date
    Jul 2012
    Posts
    3
    Post Likes
    Thread Starter
    Quote Originally Posted by teddy bear View Post
    Climate region and more detail on the construction?
    Regards TB
    Aluminium Frame Extrusion. The unit frame construction shall consist of nylon glass-fiber reinforced corner-joints that connect extruded aluminium profiles. The aluminium frames shall be gasketed along the perimeter with closed cell heavy duty neoprene rubber gasket located in between panels and the aluminium frames.

    Climate region is KSA. Around 50 degrees in summer or even a bit more.

    is any insulation inside the frames needed?

    please advise

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,844
    Post Likes
    I take it that KSA, is in Saudi. And summer temp of 50, is 50C/122F?
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Feb 2012
    Location
    New York City
    Posts
    106
    Post Likes
    This sounds like it could be a typical thermally broken construction. The panels would overlap the frame on the unit interior so the frame isn't exposed to the air stream and the neoprene gasket helps break things a bit. If you're in Riyadh, for example or the AHU is indoors it doesn't matter that much, but in Jeddah or Makkah, for example it's a bigger issue due to the humidity. You can get external condensation on the AHU without a break. You can also run a strip of plenum rated armaflex over the exposed frame inside the AHUs if they get to the field with thru metal construction and you need to thermally break them. Nothing to be gained by foaming the voids in the frame rail extrusions.

    Is this for KAFD by any chance?
    I hope I helped!

    Feel free to contact me and other users here for more detailed assistance within the context of a contract. Advice and opinions are provided here "as-is" without any warranties, guarantees or acceptance of liability for use, misuse, or accuracy of advice given. (Gotta keep my legal team off my back at work.)

  6. #6
    Join Date
    Jul 2012
    Posts
    3
    Post Likes
    Thread Starter
    Thanks alot guys

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.