    Buffer tank job

    Lady had a 60k boiler with a 10k load. This one was tight.
    Click image for larger version. 

Name:	ImageUploadedByTapatalk1342233299.442150.jpg 
Views:	225 
Size:	34.7 KB 
ID:	276681Click image for larger version. 

Name:	ImageUploadedByTapatalk1342233320.676332.jpg 
Views:	257 
Size:	35.5 KB 
ID:	276691

  2. #2
    Join Date
    Jul 2012
    Location
    ontario canada
    Posts
    17
    as a rule i always try and mount the expansion tank in the vertical plane, maybe i'm old school as the kids say

    otherwise stellar work, i bet that boiler is way happier with the extra volume

  3. #3
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,095
    I've never heard that about exp tank but I will keep that in mind thanks.

  4. #4
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,095
    Also the boiler sounded rough until th buffer tank, then she purred. Everyone else wanted to sell them a new boiler, we said this is what you need, customer for once listened lol.

  5. #5
    Join Date
    Jul 2012
    Location
    ontario canada
    Posts
    17
    boilers are like dogs, give them a job to do that occupies them correctly and they're happy .. if you don't they usually end up peeing all over your floor

  6. #6
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,095
    Exactly ^^^^

  7. #7
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    1,652
    What is the theory? I assume the boiler was cycling on and off limit very quickly and the buffer tank allows more thermal mass to prevent this?
    ...

  8. #8
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,095
    Quote Originally Posted by kangaroogod View Post
    What is the theory? I assume the boiler was cycling on and off limit very quickly and the buffer tank allows more thermal mass to prevent this?
    To stop an oversized boiler from short cycling and premature failure. Most systems are over sized and have lots of issues.

    I have a bad feeling about this high eff oversized equipment, I see future problems.

  9. #9
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    1,652
    I have never seen or heard of this before. How is this piped? Storage tank in series with supply/return of boiler and system secondary piped?
    ...

  10. #10
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,095
    Ya it's basically the primary loop, there are 4 bungs the Side against the wall is the secondary side. They can be a pain to wire. I have to think every time I install one lol. You would be doing homeowners a service to recommend them, they also se you apart from the competition. I know we are the only shop using them, this was my second one.

  11. #11
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    6,340
    Quote Originally Posted by KlRadiant View Post
    boilers are like dogs, give them a job to do that occupies them correctly and they're happy .. if you don't they usually end up peeing all over your floor
    Haha I like that!