    mini-split indoor units

    Greetings.

    One of my customers would like to install air conditioning. They have hydronic heat and the house is relatively small. I thought that a mini-split would be ideal. The problem is that most indoor units are 35 to 45 inches wide and I just don't have a home for this. Does anyone know of an indoor unit that is about 24 inches wide. I would be installing this in a free standing closet and blowing the conditioned air out the top into a great room. I probably could install a conventional system, however, because the closet is in the living space, I am concerned about the sound level. Suggestions would be appreciated. Thanks

  2. #2
    Join Date
    May 2004
    Location
    Austin, TX
    Posts
    1,852
    Post Likes
    I can't think of a single model that is only 24" wide.

  3. #3
    Join Date
    Jul 2012
    Location
    central VA
    Posts
    229
    Post Likes
    Maybe a window unit
    I rather do nothing and be happy than to do something and not be happy

  4. #4
    Join Date
    Dec 2006
    Location
    Litchfield,Il
    Posts
    565
    Post Likes
    There has to be a place somewhere on an exterior wall. If you have that many windows your in trouble.
    If your not getting the results you desire then change. People change from either desperation or inspiration.

  5. #5
    Join Date
    Jun 2012
    Location
    Great lakes
    Posts
    41
    Post Likes
    I know I installed a mini split that was a ceiling mount, can't really rember the name brand tho. But they are out their

  6. #6
    Join Date
    May 2012
    Location
    San Diego, CA
    Posts
    352
    Post Likes
    I couldn't find one for Mitsubishi but LG has wall frames and ceiling mounted ones... I am sure all the other manufacturers do too...

    http://www.lg.com/ca_en/air-conditio...tial/index.jsp
    You can call me Sam

    It should be a crime to be a mechanical engineer in San Diego
    Summer Design Temperature: 83 F Dry Bulb ~ 69 F Wet Bulb (California Climate Zone 7)

  7. #7
    Join Date
    Jul 2012
    Location
    central VA
    Posts
    229
    Post Likes
    Mitsubishi makes a flush ceiling mount air handler unit
    I rather do nothing and be happy than to do something and not be happy

  8. #8
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    We did a 3 head Mitsu system a few months ago. Due to no place to put a wall unit, one room got a floor mount. Rather pricey but what we had to do.

  9. #9
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Is there an attic?
    If so, some of the mini split manufacturers make ducted air handlers.

  10. #10
    Join Date
    Jun 2012
    Location
    The Woodlands, Texas
    Posts
    70
    Post Likes
    I did a lot of HVAC work while I was in the US Army and most of it was with European and Asian mini split systems.

    All of the big brands (Mitsu - Fujitsu - LG) would offer you two options.

    A small air handler type unit, that would fit in an attic or a crawlspace, and feed ductwork.

    There is also what is called a ceiling recessed unit, that mounts flush with the ceiling.

    Tony

  11. #11
    Join Date
    Jun 2012
    Location
    Northern NJ
    Posts
    11
    Post Likes
    Thread Starter
    The room to be conditioned is a great room with a cathedral ceiling ... no attic. The only exterior wall has a fireplace and a pair of windows ... no space for an indoor unit. The other 3 walls are either covered with furnishings or are archways to other rooms. This is the reason that I chose to put a unit in a closet that separates the great room from another part of house. This closet is 24" deep on the interior and about 40" wide; the 24" side is adjcent to great room. I had cosidered putting a ducted evaporator in the closet, but they all seem to be 35 to 42 " wide ... thus it will not fit. I also considered using one of the ceiling mounted units that are about 24" square. To do this I would have to mount it upside down on top of the free standing closet. I understand that this will not work because drainpan will not catch condensate. Further, these units will not handle the 2 ton that I think we need.


    At this point, I think the closet will get a conventional air handler that takes air in at the bottom of the closet and blows it out the top toward the top of the cathedral ceiling. I am concerned with noise levels as the closet is only about 7' high which means the blower will be close to the supply and return to the living space. I'm considering a 2 stage compressor so it can run at a low speed most of the time an only run high when necessary. I have not found documentation concerning what controls the speed.

    Is it possible to run a mini-split compressor with an conventional air handler? I don't know what kind of control signals are available to get these 2 units to work together and to modulate speed when necessary. Further, I don' know if any manufacturer woud warranty such a configuration.

    I appreciate \your thoughts and thanks for comments to date.

  12. #12
    Join Date
    Jun 2012
    Location
    The Woodlands, Texas
    Posts
    70
    Post Likes
    Quote Originally Posted by Sir-Fixalot View Post
    The room to be conditioned is a great room with a cathedral ceiling ... no attic. The only exterior wall has a fireplace and a pair of windows ... no space for an indoor unit. The other 3 walls are either covered with furnishings or are archways to other rooms. This is the reason that I chose to put a unit in a closet that separates the great room from another part of house. This closet is 24" deep on the interior and about 40" wide; the 24" side is adjcent to great room. I had cosidered putting a ducted evaporator in the closet, but they all seem to be 35 to 42 " wide ... thus it will not fit. I also considered using one of the ceiling mounted units that are about 24" square. To do this I would have to mount it upside down on top of the free standing closet. I understand that this will not work because drainpan will not catch condensate. Further, these units will not handle the 2 ton that I think we need.


    At this point, I think the closet will get a conventional air handler that takes air in at the bottom of the closet and blows it out the top toward the top of the cathedral ceiling. I am concerned with noise levels as the closet is only about 7' high which means the blower will be close to the supply and return to the living space. I'm considering a 2 stage compressor so it can run at a low speed most of the time an only run high when necessary. I have not found documentation concerning what controls the speed.

    Is it possible to run a mini-split compressor with an conventional air handler? I don't know what kind of control signals are available to get these 2 units to work together and to modulate speed when necessary. Further, I don' know if any manufacturer woud warranty such a configuration.

    I appreciate \your thoughts and thanks for comments to date.

    Most mini-splits, have what are known as inverter style compressors. This is how they work.

    They convert the 240v, 60hz AC, into DC. Then they INVERT that DC into 240V AC, 5 to 120 HZ.

    This allows the compressor to be almost INFINITELY variable. When the room cools down, it cranks down to 5 HZ and just trickles in the refrigerant.

    Because of this, you will not be able to interface it with a normal air handler.


    Most of the big Mini Split manufactures, however, make small air handler type units.

    They also have outdoor condensing units, that can connect up to 8 (the most that I have seen) indoor units.

    You might also want to check out a product from LG, called their ART COOL.

    It is an indoor unit that mounts on an interior wall, that looks like a picture frame. Well, it is an actual picture frame, and you can put whatever picture you want in there.

    it is about 4 to 8 inches thick and it looks nice if placed well.

    It also gets up into the 20 SEER range.

    If you have anymore questions, please feel free to ask.

    Tony

  13. #13
    Join Date
    Jun 2011
    Location
    New Mexico
    Posts
    18
    Post Likes
    Mitsubishi makes a 2-ton vertical air handler that is 18" wide and 21" deep. It would connect with a 3-ton condensing unit. It is from their City Multi line, which allows multiple evaporators with a single condenser.

    http://usa.mylinkdrive.com/uploads/d..._Submittal.pdf

    http://usa.mylinkdrive.com/uploads/d..._Submittal.pdf

  14. #14
    Join Date
    Mar 2010
    Location
    Kent, WA.
    Posts
    218
    Post Likes
    fujitsu makes a unit called slim duct. im sure mitsu and the other ductless manufacturers make similar system. they are designed for minimal ductwork like in a wall with a low return and high discharge. or in a sofit where somebody might want some nice linear diffusers.

  15. #15
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    Quote Originally Posted by Dustykyle View Post
    I know I installed a mini split that was a ceiling mount, can't really rember the name brand tho. But they are out their
    Mitsubishi, or panosonic, I did one in a coffee over people's head, not fun

  16. #16
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    Coffee shop

  17. #17
    Join Date
    Jun 2012
    Location
    Northern NJ
    Posts
    11
    Post Likes
    Thread Starter
    jb-eng: That unit looks like it might work. I've heard that the city-multis are pricy. I'll check on that.

    hotrodrob: I looked at the duct units, but they are 35 to 43" wide and will not fit.

    Thanks for suggestions.

  18. #18
    Join Date
    Jun 2012
    Location
    Northern NJ
    Posts
    11
    Post Likes
    Thread Starter
    Tony ... The variable speed capability of inverter technology is why I think a mini-split is applicable in this case. I would like to know what acturally controls the speed; is it temperature, line pressure or ??

    Thanks.

  19. #19
    Join Date
    Jun 2011
    Location
    New Mexico
    Posts
    18
    Post Likes
    Sir-Fixalot: I can't speak to how other manufacturers do it, but from the Mitsubishi classes I have been to, it seems like the mini split inverter compressors are controlled based on temperature sensors. There are thermistors for ambient air, outside coil temp, compressor discharge temp, indoor coil refrigerant entering temp, indoor coil refrigerant leaving temp and room temp.

    The outdoor unit communicates with the indoor unit and reads the indoor temps and adjusts speed and LEV position to attempt to maintain a specific change in refrigerant temp based on how far the room temp sensor is from the setpoint.

    Since this is a communicating system, it would be difficult to "trick" the condenser into working with another type of fan coil. Maybe if you had all the boards and sensors from a proper indoor unit? Still seems risky to me.

    Good luck. This seems like a tough one.

  20. #20
    Join Date
    Dec 2009
    Location
    Bristol NH
    Posts
    229
    Post Likes
    Quote Originally Posted by Sir-Fixalot View Post
    Greetings.

    One of my customers would like to install air conditioning. They have hydronic heat and the house is relatively small. I thought that a mini-split would be ideal. The problem is that most indoor units are 35 to 45 inches wide and I just don't have a home for this. Does anyone know of an indoor unit that is about 24 inches wide. I would be installing this in a free standing closet and blowing the conditioned air out the top into a great room. I probably could install a conventional system, however, because the closet is in the living space, I am concerned about the sound level. Suggestions would be appreciated. Thanks
    If this house has a basement with room maybe consider a unico system. They are high velocity with 2" supplies, very discreet use the closet as a return. If they are installed properly they work very well and would be much quieter than an air handler in the living space. Just round pipe for the trunk line ( they call it the Plenum)

    Sent from my SCH-I500 using Tapatalk 2

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •