    High liquid line pressure

    I have a system I just installed 3 to 14 seer 410a
    ac with a 5 ton evap. coil , txv, on a furnace with a 4 to drive.
    pulled a good vacuum, and let 410a into the system.
    suction side is at 150 psi, and the liquid lie pressure is bouncing between 375-550psi.
    what the heck is going on???
    any suggestions will be appreciated.
    Thanks,
    Chris

  2. #2
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,380
    Post Likes

    high liquid line pressure

    Non condensibles

  3. #3
    Join Date
    Mar 2011
    Posts
    279
    Post Likes
    Why is this post in the job discussion forum?

  4. #4
    Join Date
    Jun 2012
    Location
    Great lakes
    Posts
    41
    Post Likes
    Did you charge the system with more freon, generally a new condenser only comes factory charged with enough freon for a15 foot line set. And if you did what was your super heat and sub cooling. Under charged system with a txv valve will give you some weird pressures.

  5. #5
    Join Date
    Sep 2010
    Location
    Western, MO
    Posts
    988
    Post Likes
    Is that a 3 ton condenser with a 5 ton coil and a four ton furnace?

    It must be my confused night.

    jim
    Common sense isn't very common anymore.

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Threads merged, please don't make duplicate threads, thank you.

  7. #7
    Join Date
    Oct 2011
    Location
    Springfield, Missouri
    Posts
    18
    Post Likes
    So in cooling is the reversing valve energized did you wire correctly. If so is txv receiving liquid or is it being bombarded with gas pockets (undercharge). Was it a new line set or was old set used and what sizes are the line sets? 410 is very very temperamental air flow must be correct and system must be correctly sized for application. You may be low on freon or gas pockets in the system that is slamming against the needle of the txv and that may be your violent swings in pressure

  8. #8
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    2,810
    Post Likes
    What's a good vacuum? Used a micron gauge or just let the pump run for a long time? If you pulled to under 500 microns and it held there with the pump off we should be able to eliminate noncondensables as the problem. If you didn't use a micron gauge then Joe is probably right.

  9. #9
    Join Date
    Oct 2010
    Location
    Calgary, Alberta
    Posts
    17
    Post Likes
    Quote Originally Posted by martyinlincoln View Post
    What's a good vacuum? Used a micron gauge or just let the pump run for a long time? If you pulled to under 500 microns and it held there with the pump off we should be able to eliminate noncondensables as the problem. If you didn't use a micron gauge then Joe is probably right.
    Yup, seen that a few times. Might have to recover, evac and recharge to rule it out for sure. Whats your comp discharge temp?

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •