    Mar 2012
    Charlotte, NC.
    feildpiece meter with admn2 monometer heat
    Anyone out there using the feildpiece meter with the admn2 monometer head? I have used mine for awhile now, I figured I would get used to it by now but that has not been the case. As soon as I get some money saved up I'm going to buy me a dual port UEI. I have several buddies with the same meter and they are telling me they don't like there's either. We are questioning the accuracy of the tool. I'm also not a huge fan of the psychrometer.
    Feb 2007
    i have the single port and if i dont zero it out just right it will give all kinds of crazy numbers.
    Mar 2012
    Charlotte, NC.
    Yep that's the same issue we are having, It takes brute force to zero the dam thing out and then it still won't go to zero. It will read .1 or .3. I sure in heck am not about to invest in any more of there accessories.
    Did you look at the spec. It may help to explain
    Fieldpiece ADMN2
    Accuracy: ±1.5% FS 0 to 50°C (32 to 122°F):
    Resolution: 0.1 or 0.01 depending on resolution selected (If 0.01 resolution is selected you must divide displayed value by 10 for actual value).
    Measurement Range: inWC: -60.0 to 60.0 mBar: -150.0 to 150.0
    If I did the numbers right thats listed accurate to about .9 inHg over the full scale.
    For comparison sake from a testo 510
    0-40 inH20 range (0 - 9999 Pascal)
    Low Range Accuracy: 3 Pa (0 to 30 Pa) or 0.01 inH2O (0 to 0.12 inH2O)
    Mid Range Accuracy: 5 Pa (31 to 100 Pa) or 0.02 inH2O (0.13 to 0.40 inH2O)
    Rest of Range Accuracy: 10 Pa +1.5% of reading or 0.04 inH2O +1.5% of reading