    If the compressor started 7 min after the condenser fan then the compressor is at fault. What is the amp draw of the compressor running? Also does it make any noises before it starts, if it does whats the amp draw. Sounds like it maybe a no pumper if the pressures stay equal.
    I rather do nothing and be happy than to do something and not be happy

  2. #15
    Join Date
    Dec 2011
    Location
    bedford ind
    Posts
    1,095
    Post Likes
    Also, no king valves, just regular. The unit would not pull down below 60,with the high side shut. Both valves were fully open to start.

  3. #16
    Join Date
    Jul 2012
    Location
    central VA
    Posts
    217
    Post Likes
    Also is this a heat pump, if so remove the O wire and see what the pressures do maybe the reversing valve is not all the way in cool mode
    I rather do nothing and be happy than to do something and not be happy

  4. #17
    Join Date
    Dec 2011
    Location
    bedford ind
    Posts
    1,095
    Post Likes
    I didn't do an amp draw after the behavior of the compressor. Sounded fairly normal on start-up. I did an amp draw before the compressor came on and it was .09, for the fan.

  5. #18
    Join Date
    Dec 2011
    Location
    bedford ind
    Posts
    1,095
    Post Likes
    Straight a/c

  6. #19
    Join Date
    Dec 2011
    Location
    bedford ind
    Posts
    1,095
    Post Likes
    The unit pumps down. both sides. The pressures were about 39 lo and 64 hi when I pulled the disconnect.

  7. #20
    Join Date
    Jul 2012
    Location
    central VA
    Posts
    217
    Post Likes
    Ok the compressor is bad then. It comes on but doesn't pump refrigerant. Thats called a no pumper
    I rather do nothing and be happy than to do something and not be happy

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Quality Home Comfort Awards