    pressure problems with york

    Went out on a york call today. With unit off pressures read, lo 28 & hi 58. It was about 85 out. Started the unit up and the liquid line started to freeze all the way to the evap coil.

    I shot some r22 in and the liquid line thawed out immediately. Unit was blowing off plenty of heat but pressures would not seperate. There was about 20 degrees difference. I stopped adding r22 and the pressure started dropping, as if a major leak.

    I pull the disconnect to listen for a leak. No leak outside. The pressures had dropped to about 28 lo, & 48 hi, just before pulling the disconnect.

    After the disconnect was pulled , the pressures rose to 151 lo & 161 hi.

    I reinserted the disconnect and the pressure pulled down to 50 lo & 73 hi, in just about 3 minutes.

    The compressor was having some trouble, kind of like shuddering just a little, a couple of times.

    The o.s. unit is a york stellar series s# wfnm026603, m# h4db030s06a.

    The inside coil was a s# efws305045, m# g-ut037sa, central cooling.

    What is going on?

  2. #2
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Liquid line drier restriction.

  3. #3
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Might be in the Condenser.

  4. #4
    Join Date
    Dec 2011
    Location
    bedford ind
    Posts
    1,088
    I wondered about that, but the line froze from the service valve all the way to the coil. I expected just the point of blockage to freeze quickly, but the whole line did. thanks

  5. #5
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    3,150
    Quote Originally Posted by ironpit View Post
    Went out on a york call today. With unit off pressures read, lo 28 & hi 58. It was about 85 out. Started the unit up and the liquid line started to freeze all the way to the evap coil.

    I shot some r22 in and the liquid line thawed out immediately. Unit was blowing off plenty of heat but pressures would not seperate. There was about 20 degrees difference. I stopped adding r22 and the pressure started dropping, as if a major leak.

    I pull the disconnect to listen for a leak. No leak outside. The pressures had dropped to about 28 lo, & 48 hi, just before pulling the disconnect.

    After the disconnect was pulled , the pressures rose to 151 lo & 161 hi.

    I reinserted the disconnect and the pressure pulled down to 50 lo & 73 hi, in just about 3 minutes
    one thing i notice , i think one of your guages are off . Hook up the low side to a jug of 22 or whatever you have , then your high , and make sure they read the same.

    Look at a pressure / temp chart and see how much psi the jug should be at.

    2nd .... the unit was almost completely empty when u arrived ... maybe had half a pound in it.

    3rd ... if you only got 73 psi on the high side , you may have a junk compressor , or a big time restriction.

    Throw your amp meter on

    Is there a drier hidden inside the OD unit ?

    4th .... make sure both service port king valves are open. Get out your allen wrench and verify.

    If both were indeed all the way open , then lets do a simple compressor test , close the high side king valve , crank her up , and make sure the low side can pull down to 0

    If it does , then atleast ur compr has a potential to be repaired

    Indoor fan is working correct ?

    Lotts of air comming out vents ?

    Report back with your findings

  6. #6
    Join Date
    Jul 2012
    Location
    Dillwyn, VA
    Posts
    43
    Does the unit have a TXV at the evap coil. If it does try
    Putting the bulb in hot water and check your pressures.

  7. #7
    Join Date
    Jul 2012
    Location
    Dillwyn, VA
    Posts
    43
    Please post what your findings were

  8. #8
    Join Date
    Feb 2012
    Location
    Toronto Canada
    Posts
    1,090
    Low on Gas
    Was the Blower working?

  9. #9
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    5,468
    Quote Originally Posted by Snapperhead View Post
    Is there a drier hidden inside the OD unit ?
    Yes there was one on the inside of these units when it came from the factory.

    Whether or not it has been removed by some other tech, is another thing.
    Instead of learning the tricks of the trade, learn the trade.

  10. #10
    Join Date
    Jul 2012
    Location
    Dillwyn, VA
    Posts
    43
    Take the bulb loose from the suction line and stick it in hot water. This will open the TXV wide open and your pressure should come up.

  11. #11
    Join Date
    Jan 2010
    Location
    new orleans
    Posts
    230
    Your down stream of your restriction and probably low charge ! Look where the frost starts and there is your problem.

  12. #12
    Join Date
    Dec 2011
    Location
    bedford ind
    Posts
    1,088
    I put a new filter on, arrow pointing inside. Pulled a vacuum to below 500 microns, released the refrigerant (r22) and inserted the disconnect. The condenser fan came on immediately, the compressor came on about 7 minutes later.

    I had checked the values on the 35/5 cap. They were 34.8 and 5.0.

    The pressures were equal until the compressor came on. at first they rose, then they started dropping , maintaining about 20 psig apart until I pulled the disconnect.

    At first the unit was putting out a lot of heat, decreasing as the pressures dropped.

    The blower was putting out plenty of air.

    This time the liquid line did not attempt to freeze or sweat.
    Last edited by ironpit; 07-13-2012 at 06:53 PM. Reason: no cabinet filter

  13. #13
    Join Date
    Dec 2011
    Location
    bedford ind
    Posts
    1,088
    no txv inside

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event