    Hi, I am an hvac tech and recently installed a honeywell focuspro 6000 in a pizza place fhor a rooftop gas fired unit that is does 2 stage cooling as well as 2 stage heat. Something is up with the second stage not kicking in. I don't know if my settings are wrong when I calibrated it or what. I pretty much set the type of system that it called for in the calibration and left everything else alone. I don't know if anyone is real familiar with this on here but let me know things I could try if you are. I would really like to find an answer for these people. Thank you!
    -Brett
    Mount Airy, MD
    Thread relocated to "Tech to Tech"
    Jul 2011
    Honeywells website has all the manuels. I believe it has to be 2 degrees below setpoiunt for second stage. Is the stat calling on w2 at the unit?
    Southeastern Pa
    Quote Originally Posted by blavoie44 View Post
    -Brett
    The stat does not respond immediately. There is a deadband that is adjustable in setup. Second stage is brought on with a greater difference from setpoint. I often see a 4 degree difference before second kicks on. Stats with adaptive learning may bring second stage on as a function of time and a lack of temperature change when running first stage.
    Why do you think that the stat is not controlling the unit properly?
    Are you an HVAC tech?
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Maybe you didn't read the manual well enough . . . . .. Or what do i know, maybe you did ... But if i had a new 6000 2 stage stat not initiating a 2nd stage demand like the back of my hand i know what setting to look for before i do anything else.
    Sent from my HTC Sensation 4G using Tapatalk 2
    Southeastern Pa
    OP, were you able to ask your service manager about this???
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Jul 2012
    The second stage is kicking in but shutting off sporadically during extreme temperatures.
    Jul 2012
    And what setting would that be?
    Well that setting is irrelevant at this point if now you say 2nd stage does kick in.
    Athens, Ohio
    Quote Originally Posted by chris4 View Post
    They have Mexicans on the website?
    Jul 2012
    The second stage does not come on for a long time and the unit will not keep up with the given space. The supplies are pushing out 67 degrees in the eating area and around 70 degrees by in the cooking area. they have now added two more pizza ovens, so now they have 4 ovens, so there is a lot of competition for the unit to overcome. I should be getting a temp. Of of under 60 degrees from these supplies if they are working correctly.
    What makes you think its the thermostat that is the problem?
    Did the unit cool ok before you put the new thermostat on?
    Jul 2012
    Correct, it did.