    Water heater burn up.

    Found this one today, pretty nice. Not exactly sure how it happened, I'm guessing it back fired. Also the idiots had it plumbed backwards.

    Name:  ImageUploadedByTapatalk1342126298.406068.jpg
Views: 827
Size:  49.3 KB

  2. #2
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,257
    D@MN
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  3. #3
    Join Date
    Jun 2002
    Location
    Upstate Central NY
    Posts
    526
    It did not "backfire" - you would have soot around the top of the burner opening.

    there looked to be a leak at one of the connections at the gas valve or the gas valve itself.

    We had a gas valve awhile back that was leaking out of the a seam in the aluminium casting - if conditions were right it would have ignited.

  4. #4
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,191
    Quote Originally Posted by edbrown View Post
    It did not "backfire" - you would have soot around the top of the burner opening.

    there looked to be a leak at one of the connections at the gas valve or the gas valve itself.

    We had a gas valve awhile back that was leaking out of the a seam in the aluminium casting - if conditions were right it would have ignited.
    I was thinking more along the lines of it backing up to the gas valve not out of chamber.

  5. #5
    Join Date
    Jun 2012
    Location
    San Francisco Bay Area
    Posts
    54
    wow

  6. #6
    Join Date
    Apr 2011
    Location
    Coastal Maine
    Posts
    573
    Quote Originally Posted by edbrown View Post
    It did not "backfire" - you would have soot around the top of the burner opening.

    there looked to be a leak at one of the connections at the gas valve or the gas valve itself.

    We had a gas valve awhile back that was leaking out of the a seam in the aluminium casting - if conditions were right it would have ignited.
    I agree with Ed on this one. There was a leak at the gas valve that ignited. Not a backfire.

  7. #7
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,191
    Ya I guess that makes more sense, first time I've seen this but judging by the soot it must have been.

  8. #8
    Join Date
    Dec 2007
    Posts
    3,935

  9. #9
    Join Date
    Apr 2011
    Location
    michigan
    Posts
    148
    I changed out a "Leaking" water heater yesterday, went to attach my garden hose to the drain, the drain fell off in my hand, found their "Leak" Luckily there was so much sediment in the thing that the hole was plugged and didnt spray me as the drain fell off. I have seen a few with markings similar to yours, I have had some which the gas control itself was leaking, lucky nothing else caught on fire!

  10. #10
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,191
    Quote Originally Posted by pacnw View Post
    Mobilehome, right, and outside access?
    Yep trailer. It was a sad install hot was plumbed in on the cold, it had a concentric vent, this heater wasn't setup for that, the 3" vent pipe was to short so they slid the 4" over the vent instead. Just embarrassing.

  11. #11
    Join Date
    Sep 2010
    Location
    Henrico, Virginia
    Posts
    36
    I have seen this a couple of times before. One was leaking at the Baso because it was loose and the other was leaking around the temp setting stem. More often I've found the burner tube nut loose, but I've never had one of those ignite.

  12. #12
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    5,450

    Question

    Any pics of the water piping? I see it is a bottom feeder. That means there must be a vacuum breaker at the top.

    Looks like a leak at the valve. Was the insurance contacted on this?

    What about venting?

  13. #13
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,191
    They didnt have a vacuum breaker, I put a top feed in after. The venting was not done correct either, the exaust was to short so they ran the 4" combustion air pipe over the 3" ex. The ins wasn't called it was a rental with no insurance I bet. It was by far the worst install I have seen, i know it's hard in that small area but damn it was bad.