    Thumbs up Carrier 30RA aquasnap

    Anyone expierenced alarm A140 phase reversal and existing chiller that has been running. schematic doesnt show phase protection. any recommendation other than swapping leads.and how does logic confirm phase reversal. any help will be great.

  2. #2
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Suction pressure dropping within a few seconds? What part of Texas you around?

  3. #3
    Join Date
    Jul 2003
    Location
    Texas
    Posts
    346
    Post Likes
    Thread Starter
    West Texas- El Paso area. Alarm happens intermittently, once in a while.

  4. #4
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by chillerguru View Post
    West Texas- El Paso area. Alarm happens intermittently, once in a while.
    Is it a single or dual circuit chiller?

  5. #5
    Join Date
    Jul 2011
    Posts
    12
    Post Likes
    I've seen this alarm on aquasnaps and package units that also use comfort link. I've resolved it by cleaning the transducers or once a broken wire on the suction presure swith. The controller looks at suction and discharge presure for 10 seconds and if they do not have a 50 psi difference it thinks the phases are reversed.

  6. Likes dudeabides, nutradesman liked this post.
  7. #6
    Join Date
    Jun 2007
    Posts
    1
    Post Likes
    I have a 30RA055 ton aquasnap i'm working on and the chiller seems to be generating the T051, T052, T055 & T056 alarms after about 5 hours of run time. It seems as if the 5amp circuit breaker on the control panel trips right before these alarms are generated. I tried investigating but have no luck.

    Any ideas on what this could be?

  8. #7
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    It's either a shorted contactor coil or a shorted wire. Put it in test mode and check it with an amp clamp.

    c
    Quote Originally Posted by LeroyForbes View Post
    I have a 30RA055 ton aquasnap i'm working on and the chiller seems to be generating the T051, T052, T055 & T056 alarms after about 5 hours of run time. It seems as if the 5amp circuit breaker on the control panel trips right before these alarms are generated. I tried investigating but have no luck.

    Any ideas on what this could be?

  9. #8
    Join Date
    Jul 2003
    Location
    Orange County N.Y.
    Posts
    1,186
    Post Likes
    Quote Originally Posted by chillerguru View Post
    Anyone expierenced alarm A140 phase reversal and existing chiller that has been running. schematic doesnt show phase protection. any recommendation other than swapping leads.and how does logic confirm phase reversal. any help will be great.
    The phase reversal alarm just means that the computer did not see a pressure differential on the 2 transducers when it attempted to start what ever compressor that alarm is associated with. Contactor isn't pulling in, the circuit breaker is tripped, or you have locked rotor.

    ...Ron

    Sorry for the redundancy.
    Last edited by rscamaro; 06-16-2013 at 01:32 AM. Reason: redundant post
    Roof Rat

  10. #9
    Join Date
    Dec 2005
    Location
    North America
    Posts
    299
    Post Likes
    Do you have a digital scroll compressor

  11. #10
    Join Date
    Apr 2007
    Location
    uk
    Posts
    326
    Post Likes
    Controller needs to see a pressure differential of 1 bar/min upon start up

  12. #11
    Join Date
    Apr 2006
    Posts
    337
    Post Likes
    Quote Originally Posted by chris4 View Post
    I've seen this alarm on aquasnaps and package units that also use comfort link. I've resolved it by cleaning the transducers or once a broken wire on the suction presure swith. The controller looks at suction and discharge presure for 10 seconds and if they do not have a 50 psi difference it thinks the phases are reversed.
    Dude, yours was the post that just bailed me out on this call. You saved me time and aggravation -- two of my most prized possessions. Be proud!

    Sent from my SM-N910P using Tapatalk

  13. Likes stanbyyourword liked this post.
+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •