    WaterFurnace 5 Series

    I was curious if anyone could help me. I have a WaterFurnace 5Series NDV, an Intellizone zone panel (2 zones), and the new elite communicating Tstats TPCM32U03. I keep getting the red fault screen on both Tstats with "Communication Error" on the screen. The second zone does not always open or close the zone dampers properly even though they get 24V. The NDV has only the Aurora "Base" board, not the "Advanced" board. I have the Tstats hooked up properly as "traditional" tstats(P1) not the commmunicating hookup (P7). If it matters, I work for a WaterFurnace contractor, I just would like to find a solution before my know-it-all higher-ups. Thank you.

  2. #2
    Join Date
    Jan 2010
    Location
    Fort Wayne, Indiana
    Posts
    97
    Post Likes
    Geoapprentice,

    The communicating thermostats will not work with the original IntelliZone. If the original IntelliZone is used, an analog thermostat will need to be used. If you need additional assistance, please feel free to contact our technical support staff.

    WaterFurnace International, Inc.

  3. #3
    Join Date
    Aug 2011
    Location
    PA
    Posts
    3
    Post Likes
    Thread Starter

    I was right

    Thank you for your reply, I appreciate it. It makes me feel a bit more confident in myself that I figured that out when the "higher-ups" in the company did not think of that. Thank you.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •