    I rebuilt the TXV in Addison water cooled RTU today. The bi-flow liquid line driers were installed in parallell to the main liquid line from the factory. I cut the section out and expected to find a check valve in the main line. Nope, nothing there just normal piece of 5/8 copper. Does anyone know why it would be piped liked this?

  2. #2
    Join Date
    Mar 2011
    Posts
    1,071
    Have seen two parallel driers equalling the right cubic inch single drier for the capacity of the system.

    But this system has a pipe that goes right on past the driers?

    Is this a heat pump?

  3. #3
    Join Date
    Oct 2010
    Posts
    14
    Its a WSHP. The drier is an 085S bi-flow the 5/8" copper that runs parallel with the drier is a straight shot through.

  4. #4
    Join Date
    Mar 2011
    Posts
    1,071
    Strange. So much for its use as a particulate filter!

    With wshp's if there is only one metering device , there is no true liquid line for the drier.

    If there is two metering devices with checks and bypasses , then you have a true full time liquid line.

    You know , you don't want the liquid drier in a line that could become a gas / liquid mixture between the metering device and the feeder tubes. Probably too much pressure drop would effect evaporator performance.