Results 1 to 7 of 7
    Frown
    How do you duplicate jci PMI ,latch/unlatch logic on BI's with jace logic?
    you lost me
    Code, a little Site history. removed NCM, added FX-40. site has JCI/n2open devices.
    Is it possible to duplicate the latching feature of PMI with AX programing. example would be a binary input from aux contacts on a auto resetting low limit on a air handler. I want the input to latch on trip until a operator has seen problem, leaving ahu in failsafe position even if low-limit has reset itself. I need the ability to unlatch, thus reseting low-limit from workstation. I dont want these units on/off constantly in freeze condition.
    how can I add functions("latching feature") to the action tab for a booleen point/binary input? thanks,
    Freddy
    USe a NAND latch?
    You could use a basic latch with ANDs or ORs.
    Look in google for and SR latch. It should be basically the same thing.
    Have you looked at the Latch Function block yet?
    Yes, I have checked out the latch function block, problem lies with the BI's. What values (pins) are commandable, have not had any luck at all.
    pins?
    Wont a boolean writable work for you?
    I must not fully understand what your saying