07-12-2012, 10:55 PM #14
-
07-13-2012, 07:30 AM #15
Thanks for all the replies. I have seen this on the RTAA's also but thought they would have learned from their mistakes on the new design. I hate to "rig" a 1.5 year old machine but you gotta do what you gotta do. I am sending some pics to their (customers) M.E. so they can handle it internally and give the go ahead.
Its still just sad to see Their stuff getting hammered lately with design flaws. I generally like the equipment but between these repeated c and e coil failures, still having more headers stopping up on the new Voyagers and this issue, customers are grumbling a lot.
-
07-13-2012, 08:32 AM #16
Aside from the occasional sensor and condenser fan motor I've had little problems with my RTAA's.
Iv'e got 4.
Their only design flaw I see is they didn't use any type of sound attenuating equipment on them.
Yea I know you can buy a kit.
Had a Exv go bad on a 7 year old Chiller but that was it. To the guys who are getting sweating motor terminals check your oil temp when the comp is off. If it's cold liquid is migrating back to that compressor during the off cycle.
Replacing he EXVs fixed the terminal issue on one of my RTAA 110 s
Their RTU's are known for restrictions but usually the driers catch whatever it is those Comps are spitting out.
I've change far more Carrier headers than Tranes.
-
07-13-2012, 10:42 AM #17
I wouldn't really call this a design flaw on the part of Trane. Terminal condensation is something that's going to happen any time you put any kind of hermetic or semi-hermetic refrigeration compressor outdoors or in a non-conditioned space.
They have been doing some goofy stuff with some of their other equipment. The RTAC is one of the best air-cooled chillers on the market, though.
cperk, I've been lucky enough to never make a mistake like that. I don't ever want to have to tell someone that something I did just cost them $50k.Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.
"It's called the american dream because you have to be asleep to believe it" -George Carlin
"A nation of sheep begets a government of wolves" -Edward R. Murrow
"I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney
Buy american made goods & support locally owned businesses!
-
07-13-2012, 07:05 PM #18
-
07-14-2012, 12:19 AM #19
No reason a relatively small refrigeration compressor should cost as much as a car...
Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.
"It's called the american dream because you have to be asleep to believe it" -George Carlin
"A nation of sheep begets a government of wolves" -Edward R. Murrow
"I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney
Buy american made goods & support locally owned businesses!
-
07-17-2012, 09:27 PM #20
the older York YCAS compressors had issues similar to this, the terminal for the motor temp sensors would sweat and corrode or break off after time.
-
07-22-2012, 01:39 AM #21
Regular Guest
- Join Date
- Apr 2012
- Location
- So. Fl.
- Posts
- 55
On a YCAS that I serviced: did same painted with liquid rubber and then used a 3/4" flat armaflex and then pressed terminals onto armaflex. Punched-out indentations to allow for access, for checking voltage. Afterward,I spray glued around the edges of terminal box and used a piece of flat wood to hold overnight to set. It's been over a year and all is good. Sounds crazy, but it worked.
-
07-25-2012, 03:16 PM #22