    Quote Originally Posted by Tech Rob View Post
    To the OP, I have had to paint the motor terminals on RTAAs and RTACs with liquid electrical tape before. It's a good fix. It's easiest if you take the leads off the motor, just make sure you don't disturb the terminals themelves. Put the leads back in the right place or you'll be buying a new $20,000 compressor.
    Are you speaking from experience? That's the best way to learn. LOL!

  2. #15
    Join Date
    Jan 2002
    Posts
    247
    Thanks for all the replies. I have seen this on the RTAA's also but thought they would have learned from their mistakes on the new design. I hate to "rig" a 1.5 year old machine but you gotta do what you gotta do. I am sending some pics to their (customers) M.E. so they can handle it internally and give the go ahead.

    Its still just sad to see Their stuff getting hammered lately with design flaws. I generally like the equipment but between these repeated c and e coil failures, still having more headers stopping up on the new Voyagers and this issue, customers are grumbling a lot.
    Two wire hook up, three wire f**k up.

  3. #16
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Aside from the occasional sensor and condenser fan motor I've had little problems with my RTAA's.

    Iv'e got 4.

    Their only design flaw I see is they didn't use any type of sound attenuating equipment on them.

    Yea I know you can buy a kit.


    Had a Exv go bad on a 7 year old Chiller but that was it. To the guys who are getting sweating motor terminals check your oil temp when the comp is off. If it's cold liquid is migrating back to that compressor during the off cycle.

    Replacing he EXVs fixed the terminal issue on one of my RTAA 110 s

    Their RTU's are known for restrictions but usually the driers catch whatever it is those Comps are spitting out.

    I've change far more Carrier headers than Tranes.

  4. #17
    Join Date
    Mar 2007
    Posts
    3,108
    I wouldn't really call this a design flaw on the part of Trane. Terminal condensation is something that's going to happen any time you put any kind of hermetic or semi-hermetic refrigeration compressor outdoors or in a non-conditioned space.

    They have been doing some goofy stuff with some of their other equipment. The RTAC is one of the best air-cooled chillers on the market, though.

    cperk, I've been lucky enough to never make a mistake like that. I don't ever want to have to tell someone that something I did just cost them $50k.
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

  5. #18
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,349
    Quote Originally Posted by Tech Rob View Post
    ...I don't ever want to have to tell someone that something I did just cost them $50k.
    hurry up and buy it! the prices are skyrocketing!
    "Mother" is the name for God on the lips and hearts of children....The Crow

  6. #19
    Join Date
    Mar 2007
    Posts
    3,108
    No reason a relatively small refrigeration compressor should cost as much as a car...
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

  7. #20
    Join Date
    Aug 2011
    Location
    York, PA
    Posts
    159
    the older York YCAS compressors had issues similar to this, the terminal for the motor temp sensors would sweat and corrode or break off after time.

  8. #21
    Join Date
    Apr 2012
    Location
    So. Fl.
    Posts
    57
    On a YCAS that I serviced: did same painted with liquid rubber and then used a 3/4" flat armaflex and then pressed terminals onto armaflex. Punched-out indentations to allow for access, for checking voltage. Afterward,I spray glued around the edges of terminal box and used a piece of flat wood to hold overnight to set. It's been over a year and all is good. Sounds crazy, but it worked.

  9. #22
    Join Date
    Dec 2010
    Location
    Down by the river
    Posts
    1,650
    Quote Originally Posted by Tech Rob View Post
    No reason a relatively small refrigeration compressor should cost as much as a car...
    I would suggest looking for new supplier of compressors
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event