    what gas does this walk in take from pressures

    Found and fixes leak. Can anyone tell me what gas this walk in Cooler takes from these pressures?

    Condenser fan cut in 200 diff. 35

    Compressor cut in 28 diff. 20
    High pressure cut out 350

    There is also a temperature control in the walk in.
    The more you know, the more you realize how much you don't know.

  2. #2
    Join Date
    Jun 2007
    Location
    Pigeon Forge, TN
    Posts
    293
    Never mind. Found 134a sticker on evaporator
    The more you know, the more you realize how much you don't know.

  3. #3
    Join Date
    Sep 2010
    Location
    Western, MO
    Posts
    871
    If the tag was hard to find, I hope the last guy put 134a in it.

    If you didn't swing by and write it or add a sticker to the compressor.

    jim
    Common sense isn't very common anymore.

  4. #4
    It it's 134a, that HPC needs to be at least 100# lower and the CFM cut in lower

  5. #5
    Join Date
    Aug 2009
    Location
    Peoria IL
    Posts
    72
    Quote Originally Posted by smilies View Post
    It it's 134a, that HPC needs to be at least 100# lower and the CFM cut in lower
    i agree double check all your setting there they are off for 134a

  6. #6
    Join Date
    Jun 2007
    Location
    Pigeon Forge, TN
    Posts
    293
    Thanks for all the input. Got it going.
    The more you know, the more you realize how much you don't know.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event