    I've put in a new compressor on a med temp temperture reach in cooler, and was wondering ,would a sight glass be accurate in this system,it has a cap tube for refrigerant control.

  2. #2
    Join Date
    May 2005
    Posts
    1,225
    no. charge the thing per the info plate..
    Let's give nukes a chance.

  3. #3
    Join Date
    Jan 2006
    Location
    Near Atlanta, GA.
    Posts
    13,981
    Nope

  4. #4
    Join Date
    Aug 2006
    Posts
    10
    That won't apply here.The unit uses a bunch of coiled tubing off the high side to evaporate the water in the evaporator drain pan,it was corroded and leaking so I replaced it by coiling my own tubing so the system capacity has changed ,what about a certain super heat or a 20 degree td in coil and box temperture? I don't know ,I don't get to work on a whole lot of refrigeration.

  5. #5
    Join Date
    Nov 2005
    Posts
    570
    A sight glass would be a waste of time and money on a cap system.

  6. #6
    Join Date
    May 2005
    Posts
    1,225
    ive done the same thing doOd, it'll be close..charge it 2-3 oz under and go from there..
    Let's give nukes a chance.

  7. #7
    Join Date
    Jan 2004
    Location
    Earth
    Posts
    4,493
    Charge it on superheat, it's the only way to get it right now.
    A Diamond is just a piece of coal, that made good under pressure!

  8. #8
    Join Date
    Aug 2006
    Posts
    10

    Confused

    I'm going to weigh the charge in as close as I can then check my superheat.But why won't a sight glass work? You wan't only liquid going into the cap tube,right?

  9. #9
    Join Date
    Jan 2006
    Location
    Near Atlanta, GA.
    Posts
    13,981
    Weigh it in to get it close, get the box to temp and tweak it to about 10* superheat at temperature.

  10. #10
    Join Date
    Jun 2006
    Location
    Walla Walla
    Posts
    35

    Cool

    if you want to put a sightglass on a system with a cap tube i suggest taking a black sharpie and inking out the glass except in the middle, now you have a MOISTURE indicator.

  11. #11
    Join Date
    Jun 2006
    Location
    Walla Walla
    Posts
    35
    sorry forgot, I would charge it by superheat as well.

  12. #12
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,459
    Also keep a eye on the high side when charging by superheat dont want it to go to high. If it does before the low side comes up then replace the cap-tube. I change the cap tube alot of times when I am replacing the compressor with out even knowing if it is restricted or not. Been disappointed more than once after changing a locked or burnt out compressor only to find out the cap tube is resticted too.

  13. #13
    Join Date
    Jun 2006
    Location
    Walla Walla
    Posts
    35
    Amen kbghdg, I do the same. I always change cap tube as well even if I don't know if it is restricted. I have been bit too many times from that. Change a compressor and drier on cap tube system and charge up (evacuating of course) only to find captube restricted or runs good for a day then goes bad because the last compressor was a burn-out and it kicked some insulatin (or whatever)around and now the customer thinks it should be a free call(this is warranty right?) CYA