Water cooled walk in
I have a walk in cooler/freezer with three condenser units all cooled by city water that flows constantly around the compressors and condensers. Problem is the water exiting the system is still very cold. I fear there is a great waste of water for no reason. There is no regulator for the cold water cooling. Would like your view of what to do. Thanks
-
07-09-2012, 11:10 PM #2
Install air cooled condensers.
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
07-09-2012, 11:15 PM #3
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
[QUOTE=COVENANT HVAC;13682871 water that flows constantly around the compressors
Could you explain this ?
-
07-09-2012, 11:19 PM #4
[QUOTE=VTP99;13684561][QUOTE=COVENANT HVAC;13682871 water that flows constantly around the compressors
Could you explain this ?[/QUOTE]
Probably watercooled semi hermetics with the loop running around the bodyLocal 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
07-09-2012, 11:22 PM #5
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
-
07-09-2012, 11:27 PM #6
-
07-10-2012, 12:18 AM #7
Professional Member*
- Join Date
- Jun 2005
- Location
- Las Vegas NV
- Posts
- 1,111
-
07-10-2012, 12:28 AM #8
Professional Member*
- Join Date
- Jun 2005
- Location
- Las Vegas NV
- Posts
- 1,111
-
07-10-2012, 12:29 AM #9
New Guest
- Join Date
- Jul 2012
- Posts
- 2
Walk in cooler
Yes, they are semi herms, with the cooling lines looped around each compressor...it seems like quite a waste of water... suggestions?
-
07-10-2012, 06:42 AM #10
You need to install a pressure actuated water regulating valve on each unit and set them to maintain a pressure corresponding to 105°F SCT.
Here's some info on the valves: 125687.PDF
-
07-11-2012, 12:57 AM #11
sounds like they need water regulating valves check with city codes we can't use city water anymore
-
07-13-2012, 11:14 PM #12
Professional Member
- Join Date
- Jun 2012
- Location
- Tenn
- Posts
- 94
It should have a water regulater on the outlet side. My first question is whether or not the units are keeping temp? Most water cooled units that I have worked on are set to maintain 105 degree discharge temp from the condensor. I could tell you funny stories about how that works in the Persian Gulf or off the coast of Cuba, but the system should have a regulator on the discharge side of the condensors. If the water leaves before collecting the heat, it is defeating the purpose.