07-09-2012, 08:35 PM #14
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
Do you know the model # so I can look up the correct installation method ?
-
07-09-2012, 08:39 PM #15
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
If the solenoid does not close during defrost, refrigerant might bleed through the TXV.
-
07-09-2012, 08:41 PM #16
Regular Guest
- Join Date
- Jul 2012
- Posts
- 20
model # for the solenoid?
-
07-09-2012, 08:47 PM #17
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
No for the Kysor case. Does the solenoid valve not close during defrost ?
-
07-09-2012, 08:47 PM #18
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 918
Should have 3 defrosts for for 45 minutes if they have reversing fans in them....
Are the fans reversing in defrost?
If electric defrost 3 for 30 min.
That case that has 20 degree temp needs to be adjusted by your tech... Or the other 3 need to be.. Superheat should be all the same on them.. Or discharge air should be close to the same.
-
07-09-2012, 08:52 PM #19
Regular Guest
- Join Date
- Jul 2012
- Posts
- 20
Ksyor case M1A12U is the case number. I don't think the solenoid closes during deforst because nothing else is connected to it. I would think it would stay open because the case temp is higher and the thermostat is calling for the solenoid to open.
Dchappa21 - i called the company and they said the fans should reverse but my case do not have that relay that make them go in the other direction.
-
07-09-2012, 08:55 PM #20
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 918
Discharge air should be set for 22-26 degrees on those cases.. So if the t-stat is in the discharge air it is really close....
Guess that is for the m1a3 it's the 3000 series... Not sure how much different it is.
-
07-09-2012, 08:59 PM #21
Regular Guest
- Join Date
- Jul 2012
- Posts
- 20
http://kysorwarren.com/docs/uploaded...71001_MEAT.pdf
looks similar
45 min defrost would kill the red meat that its displayed in it.
-
07-09-2012, 09:03 PM #22
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 918
It should terminate at 45 degrees... If wired correctly
-
07-09-2012, 09:05 PM #23
What is the method of defrost? 6 times a day should be enough but 25 mins may not be long enough if its off cycle.
-
07-09-2012, 09:11 PM #24
Regular Guest
- Join Date
- Jul 2012
- Posts
- 20
-
07-09-2012, 09:19 PM #25
Off-time defrost is not recommended for M1A3 cases.
From page 13 of the manual. I bet the reverse cycle fans have all be pulled out and replaced with standard 9 watt motors over the years and now the cases have defrost issues
-
07-09-2012, 09:24 PM #26
Regular Guest
- Join Date
- Jul 2012
- Posts
- 20
it just started in the past couple of months.... was working fine with just regular fans defrosting but i have to say in the past 3 years the coils stayed clean as i can tell for all but the furthest unit from where the line comes in to the case. problems started when we called someone out to "fix" the last case that would ice up every 3 months and the messed them all up