    Kysor Warren Single Deck Meat Case

    Model M1A 12' long about 48' total

    5hp compressor running 409a gas

    I have a problem that none of the local repair tech are able to figure out. Even called in tech that KysorWarren recommended and still nothing.

    Problem are 2 front -
    Can not get the product temp below 40 degrees.
    Evaporator is freezing up within 2 days of getting all the ice off it.

    This unit has been in this building almost 25 years.

    there are 6 - 25 min defrost cycle put in by the last tech. who also adjusted the superheat at each section of the open single deck meat case. he also checked the humidity in the store and it was around 45. there are no ducts blowing air on the case. the store temp does go above 75 to maybe 78.

    the thermosatat is hooked up to a solenoid that is on the return line and that's all the controls the configuration.

    the liquid line is cold and has a little frost right below the case i am not sure what else to do. Have been spending a lot of money and have no results.

    I have to get the product below 40. and get the ice off the coils.

    anyone able to repair this i am at zipcode 31021

  2. #2
    Join Date
    Jan 2010
    Posts
    6,209
    [QUOTE=dilvala;13681361]Model M1A 12' long about 48' total


    the liquid line is cold and has a little frost right below the case

    I would look here for your problem.
    *****He corrected the line type.*****
    Last edited by VTP99; 07-09-2012 at 07:45 PM. Reason: Noted Above

  3. #3
    Join Date
    Jul 2012
    Posts
    20
    [QUOTE=VTP99;13681451]
    Quote Originally Posted by dilvala View Post
    Model M1A 12' long about 48' total


    the liquid line is cold and has a little frost right below the case

    I would look here for your problem.
    its the bigger of the 2 pipes going to and coming from this case. not sure if that's the liquid line

  4. #4
    Join Date
    Jan 2010
    Posts
    6,209
    [QUOTE=dilvala;13681561]
    Quote Originally Posted by VTP99 View Post

    its the bigger of the 2 pipes going to and coming from this case. not sure if that's the liquid line
    That would be the suction line not liquid. How many TXV's are there ?

  5. #5
    Join Date
    Jul 2012
    Posts
    20
    [QUOTE=VTP99;13681581]
    Quote Originally Posted by dilvala View Post

    That would be the suction line not liquid. How many TXV's are there ?
    4 one for each 12' section

  6. #6
    Join Date
    Jan 2010
    Posts
    6,209
    The case did work correctly at one time yes ?
    R409 would run at about 22 psig. Do you know what that suction pressure was ?
    Did he check all 4 TXV's ? What did he set them at ?
    Does the system have a sight glass ?

  7. #7
    Join Date
    Jul 2012
    Posts
    20
    model # for the solenoid?

  8. #8
    Join Date
    Jan 2010
    Posts
    6,209
    No for the Kysor case. Does the solenoid valve not close during defrost ?

  9. #9
    Join Date
    Jul 2012
    Posts
    20
    Ksyor case M1A12U is the case number. I don't think the solenoid closes during deforst because nothing else is connected to it. I would think it would stay open because the case temp is higher and the thermostat is calling for the solenoid to open.


    Dchappa21 - i called the company and they said the fans should reverse but my case do not have that relay that make them go in the other direction.

  10. #10
    Join Date
    Jul 2012
    Posts
    20
    http://kysorwarren.com/docs/uploaded...71001_MEAT.pdf



    looks similar




    45 min defrost would kill the red meat that its displayed in it.

  11. #11
    Join Date
    Sep 2007
    Location
    NH
    Posts
    1,146
    It should terminate at 45 degrees... If wired correctly

  12. #12
    Join Date
    Apr 2007
    Location
    Loris SC
    Posts
    208
    What is the method of defrost? 6 times a day should be enough but 25 mins may not be long enough if its off cycle.

  13. #13
    Join Date
    Jul 2012
    Posts
    20
    Quote Originally Posted by refertecbd View Post
    What is the method of defrost? 6 times a day should be enough but 25 mins may not be long enough if its off cycle.
    air defrost with compressor turned off with a defrost timer

Page 1 of 4 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event