Kysor Warren Single Deck Meat Case
Model M1A 12' long about 48' total
5hp compressor running 409a gas
I have a problem that none of the local repair tech are able to figure out. Even called in tech that KysorWarren recommended and still nothing.
Problem are 2 front -
Can not get the product temp below 40 degrees.
Evaporator is freezing up within 2 days of getting all the ice off it.
This unit has been in this building almost 25 years.
there are 6 - 25 min defrost cycle put in by the last tech. who also adjusted the superheat at each section of the open single deck meat case. he also checked the humidity in the store and it was around 45. there are no ducts blowing air on the case. the store temp does go above 75 to maybe 78.
the thermosatat is hooked up to a solenoid that is on the return line and that's all the controls the configuration.
the liquid line is cold and has a little frost right below the case i am not sure what else to do. Have been spending a lot of money and have no results.
I have to get the product below 40. and get the ice off the coils.
anyone able to repair this i am at zipcode 31021
-
07-09-2012, 07:25 PM #2
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
[QUOTE=dilvala;13681361]Model M1A 12' long about 48' total
the liquid line is cold and has a little frost right below the case
I would look here for your problem.
*****He corrected the line type.*****Last edited by VTP99; 07-09-2012 at 07:45 PM. Reason: Noted Above
-
07-09-2012, 07:33 PM #3
Regular Guest
- Join Date
- Jul 2012
- Posts
- 20
-
07-09-2012, 07:35 PM #4
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
-
07-09-2012, 07:36 PM #5
Regular Guest
- Join Date
- Jul 2012
- Posts
- 20
-
07-09-2012, 07:43 PM #6
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
The case did work correctly at one time yes ?
R409 would run at about 22 psig. Do you know what that suction pressure was ?
Did he check all 4 TXV's ? What did he set them at ?
Does the system have a sight glass ?
-
07-09-2012, 08:41 PM #7
Regular Guest
- Join Date
- Jul 2012
- Posts
- 20
model # for the solenoid?
-
07-09-2012, 08:47 PM #8
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
No for the Kysor case. Does the solenoid valve not close during defrost ?
-
07-09-2012, 08:52 PM #9
Regular Guest
- Join Date
- Jul 2012
- Posts
- 20
Ksyor case M1A12U is the case number. I don't think the solenoid closes during deforst because nothing else is connected to it. I would think it would stay open because the case temp is higher and the thermostat is calling for the solenoid to open.
Dchappa21 - i called the company and they said the fans should reverse but my case do not have that relay that make them go in the other direction.
-
07-09-2012, 08:59 PM #10
Regular Guest
- Join Date
- Jul 2012
- Posts
- 20
http://kysorwarren.com/docs/uploaded...71001_MEAT.pdf
looks similar
45 min defrost would kill the red meat that its displayed in it.
-
07-09-2012, 09:03 PM #11
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 918
It should terminate at 45 degrees... If wired correctly
-
07-09-2012, 09:05 PM #12
What is the method of defrost? 6 times a day should be enough but 25 mins may not be long enough if its off cycle.
-