    Frown Low oil pressure lockout on conventional cast iron WI grocery freezer

    Looking for some help on a conventional cast iron compressor, ie grocery freezer that spewed its charge everywhere on the roof from the condensor. Currently have quote in place for condensor replacement, but customer wants unit running till approved. Added 2 gallons oil and still going out on low oil lockout. Reset then it runs for about 5 minutes and fails. Running about 30 psi on oil pressure from pump w/10 psi on suction. Even pumped down compressor, closed off, contained and checked oil transducer filter. What gives?

  2. #2
    Join Date
    Jul 2012
    Posts
    2
    Post Likes
    Thread Starter
    HVAC guy still trying to learn a lot of bells and whistles on Refrigeration, ie rack systems and such. Any help would be greatly appreciated.

  3. #3
    Join Date
    Jan 2010
    Posts
    13,224
    Post Likes
    What make is the oil control ?
    Sentronic ?

  4. #4
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,307
    Post Likes
    Quote Originally Posted by ir.hvac View Post
    Looking for some help on a conventional cast iron compressor, ie grocery freezer that spewed its charge everywhere on the roof from the condensor. Currently have quote in place for condensor replacement, but customer wants unit running till approved. Added 2 gallons oil and still going out on low oil lockout. Reset then it runs for about 5 minutes and fails. Running about 30 psi on oil pressure from pump w/10 psi on suction. Even pumped down compressor, closed off, contained and checked oil transducer filter. What gives?
    Cast iron comp ? Im guesing its a copeland semi hermetic. Provide the model # and there are some super sharp refrigeration guys that could give you the original oil charge and the oil pres.

    If its a sentronic I think cut out is around 8 and cut in is around 16. There should be a red and green LED thst can give you an indication of either low oil or oil pressure fluctuations.

    Also the correct way to check oil pressure is with crank case pressure, not suction.

  5. #5
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,675
    Post Likes
    Check the pump intake screen.



  6. #6
    Join Date
    Jan 2010
    Posts
    13,224
    Post Likes
    Cut-Out 7-9 PSID ( pounds sq. inch differential )
    Cut-In 12-14 PSID
    Time Delay 120 seconds +or- 15

    If your getting 20 PSID ( 30-10 ) you should not be tripping out.
    As (6) said you should be checking at the crankcase.

    Sentronic speaking