Low oil pressure lockout on conventional cast iron WI grocery freezer
Looking for some help on a conventional cast iron compressor, ie grocery freezer that spewed its charge everywhere on the roof from the condensor. Currently have quote in place for condensor replacement, but customer wants unit running till approved. Added 2 gallons oil and still going out on low oil lockout. Reset then it runs for about 5 minutes and fails. Running about 30 psi on oil pressure from pump w/10 psi on suction. Even pumped down compressor, closed off, contained and checked oil transducer filter. What gives?
-
07-08-2012, 11:04 PM #2
New Guest
- Join Date
- Jul 2012
- Posts
- 2
HVAC guy still trying to learn a lot of bells and whistles on Refrigeration, ie rack systems and such. Any help would be greatly appreciated.
-
07-08-2012, 11:24 PM #3
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
What make is the oil control ?
Sentronic ?
-
07-09-2012, 12:01 AM #4
Cast iron comp ? Im guesing its a copeland semi hermetic. Provide the model # and there are some super sharp refrigeration guys that could give you the original oil charge and the oil pres.
If its a sentronic I think cut out is around 8 and cut in is around 16. There should be a red and green LED thst can give you an indication of either low oil or oil pressure fluctuations.
Also the correct way to check oil pressure is with crank case pressure, not suction.
-
07-09-2012, 06:13 AM #5
Check the pump intake screen.
-
07-09-2012, 07:08 PM #6
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
Cut-Out 7-9 PSID ( pounds sq. inch differential )
Cut-In 12-14 PSID
Time Delay 120 seconds +or- 15
If your getting 20 PSID ( 30-10 ) you should not be tripping out.
As (6) said you should be checking at the crankcase.
Sentronic speaking