    Trane chiller

    I am installing a RTWA 125 ton used chiller and was wondering if it matters whitch way the condincing water flowes and if you can move the crossover tube that connects the two barrowes to the other side Thanks Dan

  2. #2
    Join Date
    Dec 2009
    Location
    israel
    Posts
    22
    Hi
    check the instalation manual that came with the unit.
    if i remember it shouldnt be a problem but that depends on site
    you would have to move the sensors to .
    check with a trane rep to be 100 % sure
    good luck

  3. #3
    Join Date
    Sep 2008
    Location
    A land down under
    Posts
    311
    For RTWA the counterflow subcooler design requires non-interchangeable waterboxes so if you want it to work correctly water connections are right side when facing the control panel - direction of flow is also critical for unit performance. Refer pages 18-21 of attached.
    Attached Files Attached Files
    Necessity is the mother of invention

  4. #4
    Join Date
    Mar 2008
    Location
    NC
    Posts
    1,461
    old thread. I think if this guy still has questions he might want to consider another line of work.

  5. #5
    Join Date
    Sep 2008
    Location
    A land down under
    Posts
    311
    I agree, sorry didn't look at the date of the OP. The reply came up as a new post but was thinkin this is an old chiller to be installing on a new site.
    Necessity is the mother of invention

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event