    I was brought in as a second set of eyes on this one.Got a 2 ton r410 txv system 10 degree s/c 13 degree s/h with a 15-16 degree temp drop across coil.the system will only cool down to 74 degrees on a 80-85 degree day.i checked everything,airflow,filters,coil and all were good this is the first season the customer used this system as they just bought the home and of course it was a as is sale.the customer wants a little more out of the system but funds are an issue.they were told the system was a tad undersized which i agree with.there fix was to put a 2.5ton condensing uniton the coil that was there i said i would change coil to 2.5 ton,so which is going to get more bang for the buck and again a system changout is not in the works and all the customer is looking for is about 3-4 degree colder inside temp
    Nov 2000
    Eastern PA
    I really tried, but I still don't think I quite have the full situation straight from the way it is worded.
    Did they already have a 2.5 ton outdoor unit installed without changing out the indoor coil? If so, you may get away with changing the txv to match the outdoor unit.
    ...seek, and ye shall find;..
    Ecclesiastes 10:2 NIV
    Nope its a 2 ton condensing unit and 2 ton ac coil
    Dec 2011
    New Zealand
    Fit a suction/liquid line heat exchanger by the indoor coil. Move the bulb of the TXV to the outlet of the of the heat exchanger.
    This will give an increased wetted area of the evap. Lifting the SST slightly, increasing the LMTD of the coil as whole, and reducing the refrigerant pressure drop through the evap slightly.
    Fair cheap option
    As with both options you have given i would not guarantee any specific performance gains.
    Changing the outdoor will give additional cooling, but you may have consequences when ambient is not so hot. (freezing coil and or condensation on outlet grills)
    Replacing indoor only will give increased cooling, higher SST, but could reduce humidification. (good dry bulb temp, poor wet bulb)
    i am leaning towards a coil change,it cools to 74 degrees at an 83 degree and under outdoor temp so i just need a little more cooling.
    Nov 2000
    Eastern PA
    I see no capacity gain in changing the indoor coil.
    I would try lessening the load and increasing the delta-t by reducing airflow.
    I am not familiar with what barbar is talking about....or I am just having trouble understanding posts tonight.
    i put airflow on low and adjusted the charge that was my first move
    Jun 2007
    Round Rock
    Give them the proper way to fix it in the most economical matter. Changing coil isn't going to do much IMO. It's their house and their money. If you start messing with it by changing coil, moving txv or whatever. You're gonna own their POS. Sometimes it's better to walk away and not make money than trying to help and losing money and your reputation. I've walked away from several because they didn't want to do what my recommendation was to fix it.
    I like DIY'ers. They pay better to fix.
    They totaly understand i am only going to offer maybe something that might work and it will be in writing/also i do see alot of systems around here with a 1/2 ton larger coil.
    Dec 2011
    New Zealand
    Quote Originally Posted by RoBoTeq View Post
    The present coil produces superheat, this part of the coil has minimal effect on net cooling, but could be upto 20% of the coil surface area. (sorry do not know the specific of the coil). By adding a suction line heat exchanger and moving the bulb, the coil becomes fully wetted (liquid refrigerant boiling) better heat transfer.
    The superheat is given from the liquid line "increased sub cooling"
    The better heat transfer slightly increases the the SST at the comp giving an increased refrigerant mass flow. (increase nett refrigeration effect)
    The sub cooling reduces the the flash gas entering the evap, less flash gas, reduces the pressure drop across the refrigeration circuitry.So the boil refrigerant temp is more even across the coil.
    Dec 2011
    New Zealand
    Quote Originally Posted by splus View Post
    So when you lowered your airflow, did your suction pressure drop?
    If so then you reduced the nett cooling effect, even though your air temp would seem to be colder.
    pressure dropped 4psi air temp only dropped 1 degree though
    Dec 2011
    New Zealand
    So you actually lost about 3-4% in nett cooling by reducing your airflow. Due to reduced refrigerant mass flow.