    REPLACING REFRIGERANT CONTROLS WITHOUT REMOVING CHARGE

    I was looking at a Manitowic service manual today and found this " This is a required in-warranty repair procedure " using a pinch-off tool. I have one but never use it. Anyone out there using one ?

  2. #2
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Manitowoc recommends a pinch-off & re-rounding tool for replacing stuff like the fan cycle or high pressure control. I've used one for years, more often to add service access valves to True units and such.

    Here's a past post on that tool:

    http://hvac-talk.com/vbb/showpost.ph...32&postcount=5

    (The Ritchie P/N is #60665)

  3. #3
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    I have a pinch off tool, but have never used it on a live system. Just scrap copper in my Van and when I re-round it, it never resumes it's original round shape...it definitively re-opens the pinch off, just not round.

    You able to make them round again Ice?

  4. #4
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by Phase Loss View Post
    I have a pinch off tool, but have never used it on a live system. Just scrap copper in my Van and when I re-round it, it never resumes it's original round shape...it definitively re-opens the pinch off, just not round.

    You able to make them round again Ice?
    Mine come out maybe "75% round" which is fine for a pressure control or access valve. The trouble I've seen is the pinch point is weakened and so it may fail due to vibration. I've had good luck with building up the pinch point with a little silphos to stiffen it a bit.

  5. #5
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Thread Starter
    The first and last time i used my i was trying to remove a condensing unit. On the 1/4" liquid line it would not seal it off. When i cut the line it keep spewing out. I tried to pinch it down more and it ended up cutting it.
    Also are you even a little concerned about welding a charged system ?

  6. #6
    Join Date
    Dec 2007
    Location
    houston, texas
    Posts
    3,787
    Post Likes
    If you have the room I pinch it twice about an inch apart. They never come out round but it can save you a lot of time.
    I'm not tolerating Political Correctness anymore, from now on it's tell it like it is.

    Veto Pro Pak - The best tool bag you'll ever own






  7. #7
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by VTP99 View Post
    The first and last time i used my i was trying to remove a condensing unit. On the 1/4" liquid line it would not seal it off. When i cut the line it keep spewing out. I tried to pinch it down more and it ended up cutting it.
    Also are you even a little concerned about welding a charged system ?
    When you braze on an access valve, it's not on the charged side of your pinch-off point...so it's not a problem.

    As for adding some braze to build up the re-rounded portion, I don't see that as a particular problem.

    I've never cut one off with the pinch-off/re-rounding tool, but I know I've come close...hence the buildup of brazing material suggestion.

    Quote Originally Posted by Texas-Tech View Post
    If you have the room I pinch it twice about an inch apart. They never come out round but it can save you a lot of time.
    I've done that a couple of times when I can't get the first one to hold for whatever reason. Good tip.

  8. #8
    Join Date
    Apr 2007
    Location
    Scottsdale,AZ
    Posts
    80
    Post Likes
    I use pinch off tools regularly. Lots of tools out there but not all are good for service. I always look for a aset that doesn't touch in the pinch area. Mine round well and have never had a problem. Imperials.

  9. #9
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,719
    Post Likes
    I actually saw a Manitowoc CVD unit that some hack had replaced the headmaster by using 3 pinch off tools... lame! It wasn't flowing enough during harvest, maybe because pipe only re-rounded 50% or maybe because he used an off the shelf part with 180# set point... Either way that was pretty interesting to see!

    I have used pinch off tools a lot for sealed system access. But I don't like to use them on discharge lines like for a rooftop condensing unit because I've been on at least 3 calls where a discharge line access valve broke at the pinched off section.

    Anytime I pinch off for a sealed system, once I recover, I cut out the pinch-off section.

  10. #10
    Join Date
    Feb 2008
    Location
    Guam
    Posts
    168
    Post Likes
    I have used one for years , never had a problem with them, but mainly use them for true boxs and manitiwocs as others have mentioned.

    3 pinch off tools to change a headmaster? why didnt' I think of that
    Love makes the world go around but cash pays the bills

  11. #11
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Thread Starter
    O.K. after seeing your commits here next opportunity i'll give it another go. One more thing comes to mind. Are we not worried about trapped AIR ?

  12. #12
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Thread Starter

    Thumbs up

    Quote Originally Posted by Texas-Tech View Post
    If you have the room I pinch it twice about an inch apart. They never come out round but it can save you a lot of time.
    I don't know why i didn't think of doing that.

  13. #13
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by VTP99 View Post
    O.K. after seeing your commits here next opportunity i'll give it another go. One more thing comes to mind. Are we not worried about trapped AIR ?
    If Manitowoc wants you to replace in-warranty controls this way, let them worry about the trapped air.

    For access valves, I just do a little purge after re-rounding.

  14. #14
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Thread Starter
    Quote Originally Posted by icemeister View Post
    If Manitowoc wants you to replace in-warranty controls this way, let them worry about the trapped air.

    For access valves, I just do a little purge after re-rounding.
    Good point icemeister. No problem on the purge if you forget to put to core back in.

  15. #15
    Join Date
    Apr 2012
    Posts
    3
    Post Likes
    When you braze in access ports on a true or other unit that is full of refrigerant, is there any worry about brazing a part without being able to use nitrogen? Does this cause any problems down the road with "scaling" perhaps clogging a metering device?

  16. #16
    Join Date
    Sep 2008
    Location
    Cedar Rapids, IA
    Posts
    489
    Post Likes
    Quote Originally Posted by yoyohat View Post
    When you braze in access ports on a true or other unit that is full of refrigerant, is there any worry about brazing a part without being able to use nitrogen? Does this cause any problems down the road with "scaling" perhaps clogging a metering device?
    You can squirt some nitrogen into the fittings before you braze. Even though it is not flowing it will still prevent oxidation. Also the small amount of oxidation created would be blown out by a purge after you opened the pinch. Usually you are talking about less gas than would be in a charging hose. I do question applying heat to the pinch off to dab some braze on it. That would likely produce some acid by breaking down the refrigerant.

  17. #17
    Join Date
    Apr 2012
    Posts
    3
    Post Likes
    Thanks for your reply bob_scheel.

  18. #18
    Join Date
    Oct 2009
    Location
    Raleigh, NC
    Posts
    1,022
    Post Likes
    Wouldn't applying heat to brazing temperature weaken the copper so that in the end the added brazing alloy gets your strength back to where it would have been if you had just left it alone?

  19. #19
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Thread Starter
    Quote Originally Posted by MicahWes View Post
    Wouldn't applying heat to brazing temperature weaken the copper so that in the end the added brazing alloy gets your strength back to where it would have been if you had just left it alone?
    If I was to fold a 1/4" copper tube and open it back up it would be quit weak at the kink. Pretty much what you get with the pinch-off tool. Now if you just welded the kink I would agree with you. Personally I would weld beyond that point. It would be much stronger and no different then any other weld you make.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •