Results 1 to 8 of 8
  1. #1
    Join Date
    May 2006
    Posts
    57
    Post Likes
    Current Models of A/C, Coil and furnace are as follows:
    Allegiance 10 7A0048A100A0 manufacture date 9/96
    American Standard TXHC41A4H9A0 MFR DATE “L32”


    What would the SEER rating be on this mismatch? what is the efficiency of the mismatch vs a matched ac and coil?


    the AC is a 10 SEER, with the unit being 10 years old and mistched what SEER do you think it is running at. This will help be decided if a upgrade is worth it.




  2. #2
    Join Date
    Jul 2002
    Location
    Zelienople, Pa
    Posts
    2,965
    Post Likes
    If its not in the ARI guide, there is no way to know...

  3. #3
    Join Date
    May 2006
    Posts
    57
    Post Likes
    so i guess that means not in the guide

    i wonder why the american standard AC is not in the guide.

  4. #4
    Join Date
    May 2002
    Location
    Houston Texas
    Posts
    6,380
    Post Likes
    That match will work fine you want better performance add a TEV.

    The truth is you will never know what the true SEER of any system regardless of ARI rating.

    SEER rating is based on laboratory conditions never to be reached in the field.

    Depending on your geographical location spending money oh higher ratted equipment may make sense.

    True performance of any system begins and ends with proper ductwork both supply side and return side. If your ductwork isn't properly sized sealed insulated and installed the most efficient equipment made will not function properly.

  5. #5
    Join Date
    May 2006
    Posts
    57
    Post Likes
    TEV?

    Locaton is Houston Texas

  6. #6
    Join Date
    Feb 2006
    Posts
    468
    Post Likes
    Also known as a TXV - thermostatic expansion valve. More precisely regulates refrigerant flow into evap despite different press / temp conditions indoors and out.

    Given the long cooling season and high humidity in Houston, investment to improve efficiency of AC is probably warranted, depending on electric rate and building size, thermostat setpoint.

  7. #7
    Join Date
    Jun 2006
    Location
    SW MO.
    Posts
    5,341
    Post Likes
    The primary function of a txv is to maintain a constant superheat.
    We're awl pawthetic and kweepy and can't get giwrls. That's why we fight wobots.

  8. #8
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    69,437
    Post Likes
    If system components have not been tested and rated, there is no way of knowing what you will wind up with on efficiency or capacity.

    System rating is relevant, so it does not matter if you can absolutely tell what SEER or capacity a system is. If a system with matched components is supposed to be 13 SEER and in actuallity is 10% less, then that same system with unrated components is going to be 10% less then whatever that combination may have achieved in the first place.

    Unrated systems are a crap shoot. Rated but untested system matches is nearly as bad. Stick with manufacturer's ratings of same manufacturer rated components. They are the only components that are actually tested and rated.
    ...seek, and ye shall find;..
    So always seek the Truth, not just what you want to believe to be true…
    Ecclesiastes 10:2 NIV


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech 365