Yea, I probably could have been a little more diligent about finding a company who does more thorough testing. Every time I complained, we attributed poor performance to flex duct temperature losses. Summer of 2010, the owner of the company responded: "I really dont see any issues with your system and spoke in-depth with my technician and he said it was on the money."
Of course, the thing that was on the money was the subcooling and superheat values. This seems to be a good example of - don't rely on just those values to determine if everything is working ok.
I finally started taking a better readings at the appropriate locations before and after the evaporator, started doing BTU calculations, and was able to prove that something wasn't right. Funny thing, this company still hasn't taken their own detailed return/supply temperature measurements - they are taking my numbers and passing it on to Carrier.
And I can't blame just this company, I did call someone else to get another opinion (last summer I believe). This was the guy that punched a hole in the return flex duct, took a quick measurement, compared to supply temp at nearest register and said everything was fine. I realized at this point, that this larger, Carrier dealer was not going to be able to help either.
Will post another update when I have one.
-
08-08-2012, 05:10 PM #28
Regular Guest
- Join Date
- Jul 2007
- Location
- Virginia
- Posts
- 92
Another update, and hopefully we are moving in the right direction. Finally got the Carrier service rep out here, and I was impressed - he definitely seemed to know his stuff.
He said that I need that 4" spacer between the furnace and the N coil. Even though the two are matched sizes, he said that Carrier now recommends that spacer, especially in larger systems (4 ton in my case). He said at hi stage, there really isn't enough room for air to exit the heat exchanger, and then flow into that right leg of the N coil. He said this was now in the CNPVP coil installation instructions (although I couldn't find anything in the instructions that specifically said that).
He acknowledged that I've really had this problem since day 1 (July 2007). I just could never prove it until I did my own BTU calculations.
Once the spacer is installed, hopefully I'll post my final update.
In case anyone is wondering:
Furnace: 58CVA110-20
Coil: CNPVP4821ALA
Installed July 2007
-
08-08-2012, 06:22 PM #29
Tell them to bring a compressor with them when they come out to install the spacer.
Until you get a new compressor in there, nothing else they do will make a lick of difference.If more government is the answer, then it's a really stupid question.
-
08-08-2012, 06:32 PM #30
I just looked at the current installation instructions....no mention of spacer...... and that coil is still listed as offset-able..??
It's not the Brand with the fewest repairs-It's all in the install!!! Attention to detail and using the best materials!
-
08-08-2012, 06:35 PM #31
-
08-08-2012, 06:41 PM #32
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
Was your reps initials T H ?
-
08-08-2012, 07:15 PM #33
Regular Guest
- Join Date
- Jul 2007
- Location
- Virginia
- Posts
- 92
First he looked at the furnace and coil, and had pretty much concluded that spacer was the problem, but he also talked about moving the txv sensing bulb outside the coil case.
Went outside to check superheat, and although it was < 20 (I think it was about 14F), he said he expects that to be lower - lets put that spacer in. He also verified subcooling was +/- 3 of the required 15F.
He worked out a deal with the HVAC company and agreed to pay for 4 hours of his labor and the cost of the spacer. He did no checks of the compressor and is relying on info passed to him during previous checks.
No his initials were not T H, he's a Carrier Midatlantic rep. Really seemed to know his stuff, gave me his card and email address, so in general he seemed very cooperative and helpful. I won't be too upset if he's wrong. They've gone down a path they can't back out of now (admitting that something is wrong) - they have to keep going until its fixed.
We did talk about that compressor, and the problem with Bristol TS's. He said the real problem with those has been that mechanism that engages the 2nd piston, and since amp draw is going up (although only about 50%), he says that isn't the problem.
I can't wait for the next chapter in this story.
-
08-13-2012, 04:29 PM #34
Regular Guest
- Join Date
- Jul 2007
- Location
- Virginia
- Posts
- 92
-
08-13-2012, 05:40 PM #35
I've just read this thread, I can't believe you've been this patient. I also can't beleive your original contractor hasn't condemned the compressor and fixed your problem.
-
08-13-2012, 07:03 PM #36
Just realized I'm not supposed to post here, sorry mods. Damn! That's twice!
-
08-14-2012, 09:40 AM #37
That was predicitble. Almost pathetic that a mfg rep would even recommend that as a possible solution. Clearly their goal and objective is to admit that the comressor is the problem at all cost.
Funny, we're having the same problem with a large industrial air compressor with motor. issues We're on our 3rd attempt to repair it and finally convinced them to order a different brand motor (the one we should ahve had all along for this application). Some of the fixes probably made hte problem worse. The finger pointing is truely impressive.
-
08-14-2012, 08:44 PM #38
-
08-31-2012, 09:45 PM #39
rogressem, anything new to report?
If more government is the answer, then it's a really stupid question.