    What are blower contactors, and what do they do? How does one become "pitted" and how does that affect operations?

  2. #2
    Join Date
    Jul 2006
    Location
    Southern CT
    Posts
    552
    Contactors are electrical relays. they become pitted during normal start and stop action. They are normal wear items in any unit. If the become pitted badly, they run the risk of "welding" themselves closed. If that happens, your equipment will not shut off when supposed to. And worse, if one leg welds on a 3 phase motor, you risk losing the motor.

  3. #3
    Join Date
    Jun 2006
    Location
    SW MO.
    Posts
    5,186
    [QUOTE]Originally posted by psychometric
    [B]Contactors are electrical relays. they become pitted during normal start and stop action. They are normal wear items in any unit. If the become pitted badly, they run the risk of "welding" themselves closed.

    a contactor can cause a voltage drop if too pitted, which will cause the motors to overamp a cause premature damage.
    Discipline your child so that other parents don't have to.

    We're awl pawthetic and kweepy and can't get giwrls. That's why we fight wobots.

  4. #4
    Join Date
    Jul 2006
    Location
    b'ham , al
    Posts
    23
    you can ask for a heavy duty contactor (silver contacts)