I've got a question regarding controls for a zoned system with separate heating, cooling, and ventilation systems.
The heating system (hot water baseboards) has two zones, one for the main floor and one for the basement. The A/C is a ductless system with three indoor units; one for the main floor living area, one in the finished part of the basement, and a third in the master bedroom. The HRV is obviously not zoned.
My question is, is the Honeywell IAQ VisionPro product the right choice for my application, and do these controls play nice with oil fired boilers? The specs make numerous references to multi-stage forced air systems, but I don't see hot water systems mentioned at all...
Alternatively, is there another system that would work? Ideally I'd like to have one thermostat per floor, instead of three.
Equipment:
-Peerless oil-fired hot water boiler (two heating zones)
-Mitsubishi 36kBTU tri-zone mini-split (6k/12k/18k split)
-LifeBreath HRV
-
07-07-2012, 06:21 AM #2
Professional Member*
- Join Date
- Jul 2006
- Location
- Virginia
- Posts
- 3,701
The iaq will work for the boiler and hrv ,will not work on the mitsubishi unless there is a interface module that im not aware of
-
07-07-2012, 03:23 PM #3
New Guest
- Join Date
- Jul 2012
- Posts
- 2
Thank you, if that's the case then I'll just stick with what I have.