    Quote Originally Posted by Tommy knocker View Post
    So R123 what danger exactly are you referring too? Let's try this. In your expert opinion will the oil pump produce enough vapor refrigerant pressure to fool the oil pressure transducer if no oil is in the seperator?
    No, the oil pump will not produce any vapor refrigerant pressure to fool the oil pressure transducer if no oil is in the seperator, and in that case the compressor won't start. But, once the compressor starts, the pre lube pump shuts down and at this point oil is flowing due to differential refrigerant pressure pushing the oil in the seperator, through the filters and oil solonoid valve, and on into the compressor. If the oil level runs out at this point (after the pre lube pump shuts down), then yes, the vapor refrigerant pressure could fool the oil pressure transducer. Thats why the oil level switch is in there.

  3. #43
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    Quote Originally Posted by mikeacman View Post
    for differential oil pressure the controls look at the difference between the econmizer transducer and the oil pressure transducer .....the economizer transducer is the highest low pressure in the compressor and is higher than the suction pressure ...discharge pressure drives the oil but does not factor in the oil diff calculation .... Filter diff calc yes...oil press diff ...noooooo...

    side note.. Their is about a billion software revisions .... I believe discharge pressure is watched to make sure it rises Fast enough and high enough to push the oil ...later on they started allowing the oil pumps to cycle back on if need be to eliminate nuciance shutdowns ...


    the manual used to and may still have listed the Einstein equation the controls use to prove proper oil pressure . it can be very confusing.


    If I'm wrong I'll quit the trade and go be a strip club DJ

    If i make no sense I'll sit out in the sun again tomorrow and cook my brain some more then come back for seconds....
    I think your right.

  4. #44
    Join Date
    Jun 2012
    Posts
    530
    Post Likes
    Quote Originally Posted by mikeacman View Post
    If I'm wrong I'll quit the trade and go be a strip club DJ
    After the evapco I fought today that sounds like a better career choice hahaha

  5. #45
    Join Date
    Feb 2012
    Location
    utah
    Posts
    106
    Post Likes
    I have been reading this for days and have been trying real hard to stay away but alas I cant. Carrier procedure is to add oil (1/2 gallon)to get machine to start, operate in a high load state, check ref. charge and then remove the oil.
    Now have I ever done this? let me just say that every one of my hx and gx machines have the oil level sensor wires striped at some point just wide enough for a jumper. I have never had to leave it on for more then 3 or 4 min. if you do its probably the charge or some other problem.
    in this case the tubes are probably pluged and the unit is oversized which causes it to stay in a low load condition for extended times. clean the tubes, increase the deadband, start the smaller comp first, and properly check the charge. the oil is there, run the machine properly and it will be fine.

  6. #46
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    OK so we agree that the comp is protected from no oil on start if level switch is jumped out. Now once running would vapor refrigerant absent of oil produce the pressure differential the control is looking for?

  7. #47
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by Tommy knocker View Post
    So R123 what danger exactly are you referring too? Let's try this. In your expert opinion will the oil pump produce enough vapor refrigerant pressure to fool the oil pressure transducer if no oil is in the seperator?
    I know this question is for R123 but under the right circumstances it is possible to have the control to start a compressor with the oil level switch open and the prelube just enough to make pressure.

  8. #48
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    I suppose. Sorta like a piece of straw can penetrate concrete "under the right circumstances"

  9. #49
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by Tommy knocker View Post
    I suppose. Sorta like a piece of straw can penetrate concrete "under the right circumstances"

    Sure why not , open an oil level switch next time and start a compressor and see if it starts.

  10. #50
    Join Date
    Jun 2012
    Posts
    530
    Post Likes
    Quote Originally Posted by Dallas Duster View Post
    Sure why not , open an oil level switch next time and start a compressor and see if it starts.
    "I have been reading this for days and have been trying real hard to stay away but alas I cant. Carrier procedure is to add oil (1/2 gallon)to get machine to start, operate in a high load state, check ref. charge and then remove the oil.
    Now have I ever done this? let me just say that every one of my hx and gx machines have the oil level sensor wires striped at some point just wide enough for a jumper. I have never had to leave it on for more then 3 or 4 min. if you do its probably the charge or some other problem.
    in this case the tubes are probably pluged and the unit is oversized which causes it to stay in a low load condition for extended times. clean the tubes, increase the deadband, start the smaller comp first, and properly check the charge. the oil is there, run the machine properly and it will be fine."

    ^works for him, me, and others with no catastrophe. Nobody must do it this way it is just an option. These machines are notorious for this and it is just another option. Many people do this if they are familiar with the particular machine and it's history. Say for instance a compressor was locked out for some time while another compressor was running the oil may migrate and once brought back online it would have a fit. This is just a quick tip of getting it back up and gunning.

  11. #51
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by Freightshaker View Post
    "I have been reading this for days and have been trying real hard to stay away but alas I cant. Carrier procedure is to add oil (1/2 gallon)to get machine to start, operate in a high load state, check ref. charge and then remove the oil.
    Now have I ever done this? let me just say that every one of my hx and gx machines have the oil level sensor wires striped at some point just wide enough for a jumper. I have never had to leave it on for more then 3 or 4 min. if you do its probably the charge or some other problem.
    in this case the tubes are probably pluged and the unit is oversized which causes it to stay in a low load condition for extended times. clean the tubes, increase the deadband, start the smaller comp first, and properly check the charge. the oil is there, run the machine properly and it will be fine."

    ^works for him, me, and others with no catastrophe. Nobody must do it this way it is just an option. These machines are notorious for this and it is just another option. Many people do this if they are familiar with the particular machine and it's history. Say for instance a compressor was locked out for some time while another compressor was running the oil may migrate and once brought back online it would have a fit. This is just a quick tip of getting it back up and gunning.

    So it's safe to say that you are doing performing a repair incorrectly against factory recommendation and risk and accept the consequences?

  12. #52
    Join Date
    Jun 2012
    Posts
    530
    Post Likes
    Quote Originally Posted by Dallas Duster View Post
    So it's safe to say that you are doing performing a repair incorrectly against factory recommendation and risk and accept the consequences?
    Guilty as charged I guess. I read an Evapco manual yesterday and it mentioned waxing the stainless steel components in their cooling towers. I can't really say I do that either or ever really heard of anyone doing it.

  13. #53
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by Freightshaker View Post
    Guilty as charged I guess. I read an Evapco manual yesterday and it mentioned waxing the stainless steel components in their cooling towers. I can't really say I do that either or ever really heard of anyone doing it.
    Just don't jump out the vibration switch thinking its going to wax its self.

  14. #54
    Join Date
    May 2002
    Posts
    949
    Post Likes
    Quote Originally Posted by Dallas Duster View Post
    Just don't jump out the vibration switch thinking its going to wax its self.
    ha haha ha haaa ha..

    That's a good one!!!

  15. #55
    Join Date
    Oct 2011
    Location
    South Georgia
    Posts
    141
    Post Likes
    In 1997 Carrier's engineers released a warning about jumpering the oil level switch. They stated that they had proven a lack of oil level in the seperator would allow a mixture of oil and vapor to prove differential oil pressure requirements for start up and run. In 2002 i was told by a Carlyle engineer that they had deliberately run 06N compressors without lubrication, but WITH adequate refrigerant flow thru the screws, they would last about an hour. The combination of foamed oil or no oil with low flow of refrigerant thru the screws is the killer. If you jump it out you better have good refrigerant flow thru the compressor. The compressor may not fail that day but in a few months you will be listening to a screamer with high amps.

    I speak on this with personal experience, don't do it, when in doubt put oil in the reservoir and make the machine recover oil.

  16. #56
    Join Date
    Jun 2012
    Posts
    530
    Post Likes
    Quote Originally Posted by Dallas Duster View Post
    Just don't jump out the vibration switch thinking its going to wax its self.
    I threw away the jumpers for they have sinned. I ordered a power buffer for the truck incase a customer decides to actually care for their tower before it's 5 years too late. Also tossed a lawnchair on the truck so I can sit back and enjoy the oil return safely

  17. #57
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by Freightshaker View Post
    I threw away the jumpers for they have sinned. I ordered a power buffer for the truck incase a customer decides to actually care for their tower before it's 5 years too late. Also tossed a lawnchair on the truck so I can sit back and enjoy the oil return safely
    Well at least the mechanical room floor will look shiny when the compressor fails. Then you will have some thing to fall back on.

  18. #58
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Do it don't do it it's every tech's call. I have done it. I have read it in a 30GX manual. Perhaps that manual was printed in 1996. Who knows. But it is an option. Never said jump it and leave it. It only took a few minuts when I have used this technique to get enough oil back to make the switch. Just because someone thinks they are the smartest tech in the room or they are the sole expert with the only answers that are correct does not make it so. I have several of these machines under my care and have been taking care of them for several years. I have replaced barrels and other various parts. What I have not yet had to replace is a compressor. Most of them are 1990s. Don't do it. I don't care. But don't insult people who do things different then you. Your way is not the only way. Niether is mine. But both obviously work.

  19. #59
    Join Date
    Jun 2011
    Location
    Detroit, MI
    Posts
    67
    Post Likes
    Thread Starter
    Wow...this thread sure went ape ****. It does all come down to personal procedure when dealing with servicemen. Personally, I don't jump safties unless I know they are shot AND there is a dire need for the equipment to run AND the client understands the potential consequences. A gallon of oil and piece of mind is far less expensive and easier to explain the a dead compressor- that's my motto. Following factory procedure is a great idea and a great way to cya. The 30GXR249 I initially posted about is still purring away.

    I bet the tech with the appion under the machine was trying to pump oil laden refrigerant from the cooler to the serperator with the hopes of driving the refrigerant off with the heater...thought of that one while I was there but it's a little iffy if you are at a saturated temp in the seperator- can't know if the refrigerant has boiled off.

    As I thought about the AOP on these machines I came to the conclusion it's a great idea- the York and Trane chillers I've worked on rely on discharge pressure to build fast to get oil flowing- I find it hard to believe they are fully protected every start for the first say 10 secs...of course the GXR is quite a bit smaller compressor. I like seeing all the ideas that all the oems come up with....sure a lot to learn.

  20. #60
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by Tommy knocker View Post
    Do it don't do it it's every tech's call. I have done it. I have read it in a 30GX manual. Perhaps that manual was printed in 1996. Who knows. But it is an option. Never said jump it and leave it. It only took a few minuts when I have used this technique to get enough oil back to make the switch. Just because someone thinks they are the smartest tech in the room or they are the sole expert with the only answers that are correct does not make it so. I have several of these machines under my care and have been taking care of them for several years. I have replaced barrels and other various parts. What I have not yet had to replace is a compressor. Most of them are 1990s. Don't do it. I don't care. But don't insult people who do things different then you. Your way is not the only way. Niether is mine. But both obviously work.
    The 4th sentence needs to read that this is your opinion and is not a real option.

    Just my two cent.

+ Reply to Thread
Page 3 of 5 FirstFirst 12345 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •