Thread: a/c problem everythings running but need help

  1. #21
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    64oz and the lineset was @20ft

  2. #22
    Join Date
    Jun 2004
    Posts
    946
    Post Likes
    It's almost acting like u don't have enough condenser at 350 psi.
    This is what I would check for

    Check to see how many circuit the condenser has?
    Remove condenser fan panel
    Run it with out condenser motor
    You need to feel each circuit
    Make sure they are all hot
    Just to make sure no circuit is plug

    It's not in ur liquid line cause ur high side would be lower

  3. #23
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    would it make the pressures fluctuate if the fan blade was bent . because the homeowner vacumed out the leaves he said and I was thinking maybe its not rejecting the heat but I dont know if that would fluctuate the pressures .thanks again

  4. #24
    Join Date
    Jun 2004
    Posts
    946
    Post Likes
    Brad u said this all started after a bad capacitor
    By any chance the condenser is going the wrong way?
    If wires are put in wrong on a 3 wire to run cap
    It will reverse rotation.

  5. #25
    Join Date
    Jun 2004
    Posts
    946
    Post Likes
    I can see head pressures that high and fluctuating if it's going the wrong way.

  6. #26
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    rotation correct . I was thinking probably running hot with those pressures popped the capacitor to start with.

  7. #27
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    929
    Post Likes
    Not saying this is it, but I've had two units do similar things with the fan blades in the wrong position on motor shaft. 1/2 an inch or more too low (or high though both of mine were too low) can make a difference. Check airflow with a piece of paper, move it over all fin surfaces, it should stick against coil. Any idea if the motors been changed before? Definitely seems like your having a heat rejection problem.

  8. #28
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    never been replaced but im wondering if the homeowner bent the blade cleaning out the unit

  9. #29
    Join Date
    Jun 2004
    Posts
    946
    Post Likes
    Anyone!!!!!
    I wish I was there.
    Sometimes it's hard to troubleshoot over the forum.
    I'm sure someone will be here soon.
    To straighten out both of us.

    I can tell you this much.
    If u are checking ur high side on condenser port
    And it shows that high
    Ur condenser is not doing its job.
    The flash gas to ur liquid line is what's causing ur fluctuation.
    Not enough condenser,
    Not enough air flow,
    Go ahead replace the blade
    It needs to be replace anyway, since it's bent
    It will make bearing on motor go out.

    I'll step back and see what others say

  10. #30
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    929
    Post Likes
    Quote Originally Posted by Brad gall View Post
    never been replaced but im wondering if the homeowner bent the blade cleaning out the unit
    I think you could tell if it was bent enough to matter. Did you amp fan motor and compare to nameplate.

  11. #31
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    929
    Post Likes
    Quote Originally Posted by shaka View Post
    Anyone!!!!!
    I wish I was there.
    Sometimes it's hard to troubleshoot over the forum.
    I'm sure someone will be here soon.
    To straighten out both of us.

    I can tell you this much.
    If u are checking ur high side on condenser port
    And it shows that high
    Ur condenser is not doing its job.
    The flash gas to ur liquid line is what's causing ur fluctuation.
    Not enough condenser,
    Not enough air flow,
    Go ahead replace the blade
    It needs to be replace anyway, since it's bent
    It will make bearing on motor go out.

    I'll step back and see what others say
    I agree if it's bent replace blade. Go ahead and bring a motor with you too.

  12. #32
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    should the amp draw be half of the rla on one leg I think the rla was 1.2 & .6 on one wire

  13. #33
    Join Date
    Jan 2008
    Location
    In the work truck
    Posts
    3,275
    Post Likes
    Ok I have a few questions..

    How was the unit performing prior to this year? Cool the house ok? Make set point and shut off? Did you ask the Homeowner these questions?

    Are the indoor and outdoor units a match? How old is this unit?

    Also when you evacuated the system are you using a micron gauge?
    Gotta have the right tool for the job!

    Where is all the stuff MADE IN THE USA?

    "Thats what we do Troy. Incredible, Invisible, Imbelivable things. We are an Unseen, Unknown, Unvincible fraternity of craftsman.."

  14. #34
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    ran fine 8 years, pumped down with micron guage. matched amana 2.5 ton

  15. #35
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    929
    Post Likes
    Quote Originally Posted by Brad gall View Post
    should the amp draw be half of the rla on one leg I think the rla was 1.2 & .6 on one wire
    Measured on the line wires amps should be near nameplate rating. Not half.
    Did you ever make it back to this job?

  16. #36
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    going over when I get a motor an blade just i ncase. It seems the condenseris not rejecting the heat an the condeser is clean for the amp draw to be that low???

  17. #37
    Join Date
    Jan 2012
    Location
    WEST COLUMBIA S.C.
    Posts
    293
    Post Likes
    compressor may be getting to go.the cap u replaced single or dual

  18. #38
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    dual cap 35/5/440

  19. #39
    Join Date
    Jun 2012
    Location
    Pittsburgh PA
    Posts
    57
    Post Likes
    Thread Starter
    35/5/440 dual cap

  20. #40
    Join Date
    Dec 2007
    Location
    Kansas
    Posts
    80
    Post Likes
    Fan motor maybe going out and not turning the rpms its supposed to be turning and took out the cap but still hasnt died yet.

+ Reply to Thread
Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •