Results 14 to 26 of 49
    Jul 2010
    New Jersey
    Stupid question but were you the first person there?
    I live in New Jersey and have been going on call-backs from other companies and much to my dismay I have had to remove all refrigerant and TXV if applicable I am starting to really believe guys are putting the wrong refrigerants in.
    I have been on two in this past week.
    Sucks for the customer but when I leave the systems are running beautifully
    They seem to be adding very minimal amounts but thats all it takes
    Jun 2012
    Pittsburgh PA
    changed filter drier and weigh charge in still same problem any ideas?
    Jun 2012
    Pittsburgh PA
    ive already put new 22 in but my pressures continue to fluctuate like theres non condesables. not sur what else would cause this
    Brad.
    Are you reusing same refrigerant from original problem
    Or you change it out after u pressurize it with nitrogen
    What's ur pressures this time
    Jun 2012
    Pittsburgh PA
    new 22 I charged by weight and pressure the same as the first day I was there 85suc 350liq both fluctuating @70/85 315/350
    How much did u weigh in and what does name plate say?
    Jun 2012
    Pittsburgh PA
    64oz and the lineset was @20ft
    It's almost acting like u don't have enough condenser at 350 psi.
    This is what I would check for
    Check to see how many circuit the condenser has?
    Remove condenser fan panel
    Run it with out condenser motor
    You need to feel each circuit
    Make sure they are all hot
    Just to make sure no circuit is plug
    It's not in ur liquid line cause ur high side would be lower
    Jun 2012
    Pittsburgh PA
    would it make the pressures fluctuate if the fan blade was bent . because the homeowner vacumed out the leaves he said and I was thinking maybe its not rejecting the heat but I dont know if that would fluctuate the pressures .thanks again
    Brad u said this all started after a bad capacitor
    By any chance the condenser is going the wrong way?
    If wires are put in wrong on a 3 wire to run cap
    It will reverse rotation.
    I can see head pressures that high and fluctuating if it's going the wrong way.
    Jun 2012
    Pittsburgh PA
    rotation correct . I was thinking probably running hot with those pressures popped the capacitor to start with.
Comfortech Show Promo Image
Comfortech365 Virtual Event
