  1. #1
    How do I figure out tonnage on my unit?

  2. #2
    Join Date
    Feb 2005
    Location
    Kentucky
    Posts
    57
    You can usually tell by the model of the condenser. What is the model number.

  3. #3
    Model - CKL24-1F

    Serial - 0306424230

  4. #4
    Join Date
    Feb 2005
    Location
    Kentucky
    Posts
    57
    Going by the model number it is a 2 ton. For every 12 is a ton you have a 24 for 2ton.

  5. #5
    Join Date
    Aug 2006
    Location
    Florida (some where) way-south
    Posts
    226
    that unit model looks like a 2 ton
    doing one call at a time.


  6. #6
    I have about 66 supply and a 78 return. It seems when the

    day warms up to much I'm losing. My pressures was 82 Low

    and 275 high. My UEI meter on the suction line read 48

    degree temp. Does everything sound right? The discharge

    line doesn't feel warm by hand. I'm wandering if it's

    more of an air flow problem or humidity.

  7. #7
    Join Date
    Nov 2005
    Location
    USA
    Posts
    529
    You need to call a Pro. You may have refrigerant charge issues from your readings.
    The posts and comments made by me are in no way affiliated with any company or organization. They are simply my personal opinions.

  8. #8
    Join Date
    Feb 2005
    Location
    Kentucky
    Posts
    57
    A 12 degree temp drop is low. The 82 suction psi sounds high for 78 return temp. If the suction line is 48 degrees it is slugging the compressor. What was the outdoor temp when you checked the pressures. Something is not right, is the equipment a matched system. It probably needs to be looked at.

  9. #9
    it was 94 out side.