    Ok, I in no way even brought up money. It is hot out and I was just trying to offer quick help. Did not mean to offend you or anyone on here. The reason I came to the post in the first place was because it was on google under HVAC help. So i was trying to respond so that there is a place to go and call for help that is close by,

    I understand that you are trying to offer help and everything. A lot of people who post on here can't fix it themselves either. It is a company. So even trying to work on it themselves can void warranties.

    Not sure were you are at, but if you are near Chicago, you will understand that this weather is eating people alive. I am just trying to offer help. If the installation was incorrect with the load capacity, then it may need a new unit. All I was saying is call if you need advice or help.

    I never said come buy stuff from us. I said call us for anything. Sorry.

  2. #28
    Join Date
    Feb 2010
    Location
    Cal
    Posts
    1,596
    Quote Originally Posted by Six View Post
    This forum is an amazing concept that acts like a antibiotic to all of the dishonest techs and hack workmanship that plagues our industry.
    You seem preoccupied with your crusade to promote and attach a negative stigma to OUR industry. Who does that help besides yourself? Hmmm?

  3. #29
    Join Date
    Jul 2012
    Location
    Villa Park, IL
    Posts
    6
    I am sorry if I rubbed anyone the wrong way! Really I am. I am just trying to help the ones close to us because this 100+ heat is brutal! I will keep my posts low key from now on. Sorry for the misunderstanding.

    RPM

  4. #30
    Join Date
    Mar 2012
    Location
    west burb IL
    Posts
    95
    Quote Originally Posted by Ridgeway Precision View Post
    I am sorry if I rubbed anyone the wrong way! Really I am. I am just trying to help the ones close to us because this 100+ heat is brutal! I will keep my posts low key from now on. Sorry for the misunderstanding.

    RPM
    Thanks for your offer anyway. We are now talking with the contractor about replacing an old unit as we speak and considering a larger one. But with the need to alter the ductwork, we'll most likely get the same size again.

    Quote Originally Posted by dlove
    Run those units 24/7. catch the load early and you should help slide by the 3pm heat hump.

    And close the OA dampers. completely.
    Yeah, we run the units 24/7. I'll check about our OA supply some more.

    Can't wait for this heat wave to be over. Tomorrow will be nicer and a lot better after that. Thanks a lot guys!

  5. #31
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,773
    Quote Originally Posted by ncboston View Post
    I know this is going to elicit a number of negative comments, buy I've seen water sprinklers wetting the coils to get thru extreme conditions.
    Yep, I know of a couple buildings with sprinklers set up for extreme temp days.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #32
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,773
    Might want to consider going to 2 stage 10 ton units, with the blower slowed to 320 CFM per ton. If your 7.5 ton units are moving 400 CFM per ton, that comes out to 3,000CFM. A 10 ton at 320 CFM per ton comes out to 3,200 CFM. Not a big increase in CFM.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #33
    Join Date
    Mar 2012
    Location
    west burb IL
    Posts
    95
    Quote Originally Posted by beenthere View Post
    Might want to consider going to 2 stage 10 ton units, with the blower slowed to 320 CFM per ton. If your 7.5 ton units are moving 400 CFM per ton, that comes out to 3,000CFM. A 10 ton at 320 CFM per ton comes out to 3,200 CFM. Not a big increase in CFM.
    Will this enable us to have better cooling capacity while using our current ductwork? I would think this is a great option if it does.

  8. #34
    Join Date
    Jun 2012
    Posts
    529
    Quote Originally Posted by beenthere View Post
    Yep, I know of a couple buildings with sprinklers set up for extreme temp days.
    Went to a school that had a Trane chiller with a real nice sprinkler system. All PVC with fire suppression style sprinkler heads over each coil section. It was even controlled by a pressure switch hooked up to a water solenoid valve.

  9. #35
    Join Date
    Jun 2012
    Posts
    529
    Quote Originally Posted by comfortdoc View Post
    You need more condenser capacity. If using the city water is not a big issue, you may be able to get small water cooled condensers installed in the unit. Will take some ingenuity, but use that as a supplement when conditions are above design. As mentioned, city water can destroy a fin-tube coil.
    Have a few places I would love to do that.

  10. #36
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Quote Originally Posted by btuhack View Post
    You seem preoccupied with your crusade to promote and attach a negative stigma to OUR industry. Who does that help besides yourself? Hmmm?
    You're attacking the messenger. We have a massive company in Houston that hires sales ppl. Not techs.

    The companies and techs who take advantage of ppl in a bad situation are the ones responsible.

    If I hear one more effing horror story about that group of jackass' or the usual suspects that are known for ripping ppl off Ill set up my own sting operation and put it up on youtube.

    I mean unless you have a vested interest in maintaining the status quo of selling ppl junk they dont need you should support any effort to route out companies that are in the bussiness of ripping ppl off.

  11. #37
    Join Date
    Jul 2001
    Location
    Canada
    Posts
    1,824
    If using the city water is not a big issue here we get DINGED sewage charges that are 117% of the water bill for every Gallon through the meter.

  12. #38
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,773
    Quote Originally Posted by abcando View Post
    Will this enable us to have better cooling capacity while using our current ductwork? I would think this is a great option if it does.
    Yes, While you wouldn't get the full 10 ton capacity, you'd get a lot more then you are.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  13. #39
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Quote Originally Posted by Control Man View Post
    If using the city water is not a big issue here we get DINGED sewage charges that are 117% of the water bill for every Gallon through the meter.
    It absolutely is a big issue. It s the last option for a building with a dying chiller or a building suffering through a heat wave with equipment that isn't rated for excessive ambient.

    We've done it once with full disclosure to our customer of what the consquences would be.

Page 3 of 5 FirstFirst 12345 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event