Ok, I in no way even brought up money. It is hot out and I was just trying to offer quick help. Did not mean to offend you or anyone on here. The reason I came to the post in the first place was because it was on google under HVAC help. So i was trying to respond so that there is a place to go and call for help that is close by,
I understand that you are trying to offer help and everything. A lot of people who post on here can't fix it themselves either. It is a company. So even trying to work on it themselves can void warranties.
Not sure were you are at, but if you are near Chicago, you will understand that this weather is eating people alive. I am just trying to offer help. If the installation was incorrect with the load capacity, then it may need a new unit. All I was saying is call if you need advice or help.
I never said come buy stuff from us. I said call us for anything. Sorry.
-
07-06-2012, 03:52 PM #28
Professional Member*
- Join Date
- Feb 2010
- Location
- Cal
- Posts
- 1,323
-
07-06-2012, 03:55 PM #29
Regular Guest
- Join Date
- Jul 2012
- Location
- Villa Park, IL
- Posts
- 6
I am sorry if I rubbed anyone the wrong way! Really I am. I am just trying to help the ones close to us because this 100+ heat is brutal! I will keep my posts low key from now on. Sorry for the misunderstanding.
RPM
-
07-06-2012, 04:19 PM #30
Professional Member
- Join Date
- Mar 2012
- Location
- west burb IL
- Posts
- 78
Thanks for your offer anyway. We are now talking with the contractor about replacing an old unit as we speak and considering a larger one. But with the need to alter the ductwork, we'll most likely get the same size again.
Yeah, we run the units 24/7. I'll check about our OA supply some more.
Originally Posted by dlove
Can't wait for this heat wave to be over. Tomorrow will be nicer and a lot better after that. Thanks a lot guys!
-
07-06-2012, 04:42 PM #31
-
07-06-2012, 04:45 PM #32
Might want to consider going to 2 stage 10 ton units, with the blower slowed to 320 CFM per ton. If your 7.5 ton units are moving 400 CFM per ton, that comes out to 3,000CFM. A 10 ton at 320 CFM per ton comes out to 3,200 CFM. Not a big increase in CFM.
-
07-06-2012, 06:01 PM #33
Professional Member
- Join Date
- Mar 2012
- Location
- west burb IL
- Posts
- 78
-
07-06-2012, 06:05 PM #34
-
07-06-2012, 06:08 PM #35
-
07-06-2012, 06:27 PM #36
You're attacking the messenger. We have a massive company in Houston that hires sales ppl. Not techs.
The companies and techs who take advantage of ppl in a bad situation are the ones responsible.
If I hear one more effing horror story about that group of jackass' or the usual suspects that are known for ripping ppl off Ill set up my own sting operation and put it up on youtube.
I mean unless you have a vested interest in maintaining the status quo of selling ppl junk they dont need you should support any effort to route out companies that are in the bussiness of ripping ppl off.
-
07-06-2012, 06:30 PM #37
Regular Guest
- Join Date
- Jul 2001
- Location
- Canada
- Posts
- 1,694
If using the city water is not a big issue here we get DINGED sewage charges that are 117% of the water bill for every Gallon through the meter.
-
07-06-2012, 06:38 PM #38
-
07-06-2012, 07:15 PM #39
It absolutely is a big issue. It s the last option for a building with a dying chiller or a building suffering through a heat wave with equipment that isn't rated for excessive ambient.
We've done it once with full disclosure to our customer of what the consquences would be.