    Quote Originally Posted by ncboston View Post
    I know this is going to elicit a number of negative comments, buy I've seen water sprinklers wetting the coils to get thru extreme conditions.
    We actually have sprinklers set up in 3 of our units right now. We try everything to reduce heat inside.

    Quote Originally Posted by maxster
    is the returns ducted from the space back up to the rooftop or egg crated tiles pulling the ceiling heat back?
    Yeah, the returns are ducted back to the roof toop.

  2. #15
    Join Date
    Jul 2012
    Location
    Villa Park, IL
    Posts
    6
    Rideway Precision Mechanical, Inc

    Email Addresses Removed

    Just give us a call and we can help you out!!! We will let you know what you need, and what you should do. Here to help! We are a commercial and residential HVAC company located in Villa Park!
    Last edited by Chris_Worthington; 07-06-2012 at 01:52 PM. Reason: Email Addresses Removed

  3. #16
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Quote Originally Posted by abcando View Post
    We actually have sprinklers set up in 3 of our units right now. We try everything to reduce heat inside.



    Yeah, the returns are ducted back to the roof toop.
    Excessive use of city water to cool the coils will RUIN your condenser coils.

  4. #17
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Quote Originally Posted by Ridgeway Precision View Post
    Rideway Precision Mechanical, Inc

    Email Addresses Removed

    Just give us a call and we can help you out!!! We will let you know what you need, and what you should do. Here to help! We are a commercial and residential HVAC company located in Villa Park!
    You guys going to go out and charge them to tell him what they already know ?

    That their equipment isnt rated for ambients in excess of 95 degrees ?
    Last edited by Chris_Worthington; 07-06-2012 at 01:52 PM. Reason: Email Addresses Removed

  5. #18
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,281
    Quote Originally Posted by Ridgeway Precision View Post
    Rideway Precision Mechanical, Inc

    Email Addresses Removed

    Just give us a call and we can help you out!!! We will let you know what you need, and what you should do. Here to help! We are a commercial and residential HVAC company located in Villa Park!
    Email addresses belong in your profile and NOT posted in the forum. Thank you in advance for reading the sites rules and complying with them


  6. #19
    Join Date
    Jul 2012
    Location
    Villa Park, IL
    Posts
    6
    Actually no, Sixer. The point was that he wondered if he needed to units and that he was unsure if the contractor did a proper load measurement. Sorry, was trying to help out, knowing he is in the area.

    And thanks for sarcasm. Must be the heat.

  7. #20
    Join Date
    Jul 2011
    Location
    East coast USA
    Posts
    961
    Run those units 24/7. catch the load early and you should help slide by the 3pm heat hump.

    And close the OA dampers. completely.

  8. #21
    Join Date
    May 2006
    Location
    Philadelphia, PA
    Posts
    1,383
    You need more condenser capacity. If using the city water is not a big issue, you may be able to get small water cooled condensers installed in the unit. Will take some ingenuity, but use that as a supplement when conditions are above design. As mentioned, city water can destroy a fin-tube coil.
    Climate Control Solutions for your Home or Office

    Serving Northeast Philadelphia and Surrounding Areas

  9. #22
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Quote Originally Posted by Ridgeway Precision View Post
    Actually no, Sixer. The point was that he wondered if he needed to units and that he was unsure if the contractor did a proper load measurement. Sorry, was trying to help out, knowing he is in the area.

    And thanks for sarcasm. Must be the heat.
    Who are you thanking for the free advertizing ?

    New units as a solution to high temporary load ? You guys do residential too ?

  10. #23
    Join Date
    Jul 2012
    Location
    Villa Park, IL
    Posts
    6
    I was responding to his post. And if you read his post it said they will have to get a new unit soon. So that is what I was referring to. Sorry that this post ruined your day!

  11. #24
    Join Date
    Mar 2008
    Location
    NC
    Posts
    1,460
    Quote Originally Posted by dlove View Post
    Run those units 24/7. catch the load early and you should help slide by the 3pm heat hump.

    And close the OA dampers. completely.
    I was thinking the same thing, but it's a nursing home, so they probably run them 24/7 already.

  12. #25
    Join Date
    Feb 2010
    Location
    Cal
    Posts
    1,596
    Quote Originally Posted by abcando View Post
    We are actually a nursing home facility ...
    Be careful what you post about your situation in an open forum. If someone expires due to heat or dehydration, you might make the news, or worse.

  13. #26
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Quote Originally Posted by Ridgeway Precision View Post
    I was responding to his post. And if you read his post it said they will have to get a new unit soon. So that is what I was referring to. Sorry that this post ruined your day!
    Doesn't effect me a bit. Its just unusual.

    Other guys offer up advice and warnings on this forum on a daily basis. Your advice cost $$$$.

    People come here to get away from the used car salesman that infect our industry with less than honorable sales tactics.

    To get a second opinion from techs who donate their time and knowledge because they suspect somethings not right with their equipment or the way they've been treated.



    This forum is an amazing concept that acts like a antibiotic to all of the dishonest techs and hack workmanship that plagues our industry.

    Not saying you're one of those people either so dont misunderstand.

Page 2 of 5 FirstFirst 12345 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event