    Confused

    I have a low side sitting at 90 psi and high side bouncing

    back and forth from 200 to 500 psi. The compressor amps

    is bouncing back and forth from 5 amps to 10 amps and it's

    rated at 12.1 RLA. Superheat is 15. It's 89 degress

    outside and 80 in the house. Coils fully clean and fan

    running fine. What is my problem?

  2. #2
    Join Date
    Jan 2005
    Location
    Emerald Coast
    Posts
    1,044
    Post Likes

    You need to post this in the Pro's Forum.

    ;-)

    Do not attempt vast projects with
    half vast experience and ideas.
    ...

  3. #3
    Join Date
    Jul 2000
    Location
    Louisiana , USA
    Posts
    3,280
    Post Likes
    Originally posted by stephen mendoza
    I have a low side sitting at 90 psi and high side bouncing

    back and forth from 200 to 500 psi. The compressor amps

    is bouncing back and forth from 5 amps to 10 amps and it's

    rated at 12.1 RLA. Superheat is 15. It's 89 degress

    outside and 80 in the house. Coils fully clean and fan

    running fine. What is my problem?

    This is Turtle.

    you need to bring the freon level down on it till the bouncing stoppes. On a hvac system that holds 5 pounds , 10 pounds will never fit in it. i think you have too much freon in it.

    TURTLE

  4. #4
    Join Date
    Aug 2006
    Posts
    19
    Post Likes
    Thread Starter
    Thanks Turtle. It worked.